Answer Posted / kishan
kw is indicate the mechanical energy &
kva is electrical energy. kw & kva is related to each othre
kw = kva * power factor
| Is This Answer Correct ? | 5 Yes | 3 No |
Post New Answer View All Answers
what is sevice settings for mccb?How can be it setted?
while starting a liquid starter ,is there any volage drop on water/soda on tank.can we touch the tank on starting?
Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing
What happens to a line-frequency of high-frequency transformer when it is first energized/ re-energize?
EXPLAIN WHY THE SURGE CURRENT RATING OF AN MCCB OR CIRCUIT BREAKER DECREASES WITH INCREASE IN THE RATING OF MCCB OR CIRCUIT BREAKER.
I am shobana from Chennai. I am having my personal interview on 19th Dec at Chennai.kindly mail me the questions to mail id shobana.shanthi@gmail.com
Give atleast 20 alternating current apparatus and devices.
How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?
in our all power plant have connected in grid and grid voltage and plant voltage is same, but as per as electrical concept the power will transmit from high potential to low potential but here altough same,then how power transmit from power plant to grid.
what is allowable ac mixing in dc
what is the difference between electrical choke and electronic choke?
how can you calculate fault level ?
we use 400/5A ct and 35/roor3KV,/0.1/root3KV,0.1/root3KV pt ratio. What is the multiple factor of this meter.
What happens when ac supply is given as excitation voltage instead of dc supply
What are the applications of autotransformers?