why rotor resistance starter is not suitable for
squrielcage induction motor?why it is suitable for slipring
induction motor?
Answer Posted / sennapparajan
slip ring motors normally used where ever high stsrting
torque required. by connencting external resistence through
slip rings we can increase the starting torque. so that the
motor designed with slip rings.
at normal case sqrl cage motor will be used. its rotor
conducter shorted permanently./ and to reduce this motor
starting current sar-delta sarters can be used.
| Is This Answer Correct ? | 16 Yes | 7 No |
Post New Answer View All Answers
how to handle 2500 kva transformar
Explain about 3 phase motor fault current calculation with examples?
What happen in ups if phase reverse?
can we choose current transformer secondary, to calculate residual flux in a power transformer, so as its saturation is close to the saturation level of power transformer?
What is the difference between Static and servo controlled voltage stablizer?
Dear friends I want to design busbar for1600 kva transformer(i.e2100 amps) what are all the factors to be considered before selectinga busbar what are all the standard sizes of busbars what is the formula for finding current of copper and aluminium busbar
2. What are the parameters of EHT sub-station?
If increased the frequency up to 1000 then what changes shows in voltage?
we use 400/5A ct and 35/roor3KV,/0.1/root3KV,0.1/root3KV pt ratio. What is the multiple factor of this meter.
at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?
why actual valve timing diagram is different than ideal valve timing digram of a 4 stroke engine?
WHAT IS THE PARTIAL DISCHARGE TEST?
EXPLAIN THE TERMS "INTEREST AND DEPRECIATION" AS APPLIED TO ECONOMICS OF POWER GENERATION.
Explain the operation of variable frequency transformer?
What is the difference between circuit breaker and isolator