why rotor resistance starter is not suitable for
squrielcage induction motor?why it is suitable for slipring
induction motor?
Answer Posted / sennapparajan
slip ring motors normally used where ever high stsrting
torque required. by connencting external resistence through
slip rings we can increase the starting torque. so that the
motor designed with slip rings.
at normal case sqrl cage motor will be used. its rotor
conducter shorted permanently./ and to reduce this motor
starting current sar-delta sarters can be used.
| Is This Answer Correct ? | 16 Yes | 7 No |
Post New Answer View All Answers
I WANT BHEL PREVIOUS QUESTION
Why to keep capacitor bank off while generator running.
what is the interrelation between voltage current torgue speed and magnetic flux in case of different types of electric motors
What is accuracy of a measurement?
explain why core loss of a transformer is almost constant under different load conditions when connected across a constant voltage and constant frequency.
if 6 earth pit value is 1.5 ohm then what should be the number of earth pit to make the value .8 ohm
what is the difference between linear choke and suction choke?
how to compute kAIC? with formulas...
for a 400kv t/m line with 10 ampere current will corona occur?
What is open delta Xformer? It's adavntages & Use?
what is PDU in transformer?? which company manufacture??
what is different between phase and netural
area control error
Can any one provide the inspection procedure of MIMIC for VFD panel? Details: If someone wants to have a mimic in the VFD panel what are inputs considered for the mimic(like on,off,trip) whether we are able to add speed variation in the mimic(if so how can we get) and what are the parameters to be checked in the MIMIC during inspection?
Earth has zero potential then what would be the neutral potential ?