What is difference between earth leakage relay and
restricted earth fault relay ?
Answer Posted / pratheesh
REF detects the earth faults between the transformer
secondary winding and upto the point where REF
protection CT placed. If any earth fault occurs within
this zone, REF relay will sense it.
It will not trip when any faults occurs after the
protected zone(after the REF CTs) as the earth fault
current produced in the secondaries of the REF CTs and
the Neutral Earthing CT is neutralized.
| Is This Answer Correct ? | 56 Yes | 7 No |
Post New Answer View All Answers
What is transmittance?
What is the end effect of linear induction motor ??
what happens to the water pump if ground water level is slowly decreasing?our water pump is varying from no-load full-load due to this problem
draw the full wave and half wave circuit of 3 phase system and inverter circuit used in upsĀ
how to produsing geretor power
Its possible to use 3core 2R of 240 sq.mm cable for 3phases & separely 50sq.mm 3core cable fully for Neutral for connection of PCC to MCC 3ph..4wire system?
DRAW ACIRCUIT DIAGRAM OF 100 KVA 415V/55-0-55V DELTA TO STAR TRANSFORMER
where can i get vijaya electricals limited in hyderabad interview auestions can u give me the website address plz
what is the electrical?
WHAT IS SHORT CIRCUIT STRENGTH OF 100 AMPS MCCB?
what should be the acceptrd value of winding resistance for 2.5MVA transformer
what is difference between bus coupler and auto transfer switch
What is the difference between isolators and electrical circuit breakers?
HOW WE CAN REDUCE THE CIRCUIT COMPLEX OF STAR-DELTA STARTER .BECAUSE NOW WE USING ONE TIMER RELAY & THREE CONTACTOR FOR MAIN,STAR & DELTA ?IF ANY IDEAS PLZ POST.THANK U
how to check avr of dg set of 125kva