How to calculate the diesel generator efficiency? what
details are required to identify the running diesel
generator sets with 1000 kVA & 180 kVA?
Answer Posted / m.s.srinivasan
The diesel generating set efficiency is calculated interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
| Is This Answer Correct ? | 63 Yes | 33 No |
Post New Answer View All Answers
1- What is the Polarization Index number be good for 15KV 3c#500MCM electrical cable? 2- Can I use the IEEE Std 43-2000 to perfom the PI test? Thanks
can i able to get bhel previous exam question paper?
What is inductance?
What is power factor why we should maintain the power factor unless what will happen
substation+ plc system
What is a commutator?
What is Servo Ventilated Motor?
Why PT voltages are measured with respect to ground? What do u mean by voltage or current polarized.
How to select the cable and voltage drop in circuit?
Can anybody please refer the best and simple book for about Protection relays and in detail of all its protection ?
whatare the disadvantages occur,if the form factor of transmission will not be equal to 1.11
what is conductor copnstant of ab cable
What is the formula formula for Busbar sizing and what are the things to be consider for Busbar Calculation?
What is the formuala to calculate the rating of motor protection circuit breaker
when we design electrical schemes of 11/.415kv distribution..wen and were should we show the relays??what is the function of it?for example..we place EFR Relay CT between transformer neutral link and transformer earth.Like this what are the other type of relays we should use?why?where?Explain please..Thank you