what is difference b/w HT & LT and the range of HT & LT ?

Answer Posted / mike

Less say if you had transformer in a station it was a 100kv
to 44kv the breaker between the bus an high side of the
transformer protecting it from a fault would be the high
tension. Once it leaves the low side of the transformer it
goes to a breaker that is between the transformer and the
low side bus this would be your low tension. These breakers
have ct that protect the bank with differiential relays.

Is This Answer Correct ?    12 Yes 30 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Describe the colour rendering properties of i) tungsten filament lamps ii) tubular fluorescent lamp

2629


Can anyone explain me about the RLC based Impulse high voltage generator and how to and operation of Series resonant High voltage reactor...?

1431


1 hp is equal to how much watt?

726


What is the difference between hot and cold loop testing?

676


how to calculation increase capacitor,increase power factor for three phase.

1640






DG Earth Value?

1869


what is mean by dry frequency

1945


why chock were used in old tubelights but are not newest tubelights?

1457


1.why we are using metal oxide gapless block in lightning arrester,2.What is minimum and maximum rating of metal oxide blocks using in india

1523


what are the Alarm, Trip & Safety equipment (Issues) present in Power Transformers pls Mail it to ashokbabunhce@gmail.com

1457


-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.

1580


What is online and offline ups? how does it works?

1625


what is basic difference betmeen normal & flame proof motor??

1491


8. A DYNAMOMETER TYPE WATTMETER RESPONDS TO THE.......

8505


Difference between On Line capacitor and Station Type capacitor.

1629