Answer Posted / guest
hi sanjay
1. AIR SUPPLY
I/P input - 1.4kg/cm2
Out put - 0.2 to 1kg/cm2 ok
2.input signal= 4-20 mA
i.connect the air supply to input with the hepl of REGULATOR i.e 1.4kg/cm2
ii.connect the MASTER GAUGE to OUT PUT ok
Apply the signal
i. 4mA- 0 kg/cm2 (if not Zero/0.2kg/cm2 Adjust Zero adjustment Screw)
ii. 20mA-1 kg/Cm2 (if not 1kg/cm2 Adjust Span adjustment Screw) ok.
then 8, 12, 16mA.
min. and max. is ok the remaining will perfect automatically i.e 8,12,16mA.
and MAIN IMP POINT is ON the I/P's Ckt board Side 4 adjust ment buttons is there and adjust that buttons Direct and Revese Actions ok
Is This Answer Correct ? | 20 Yes | 0 No |
Post New Answer View All Answers
What is the use of single seated valve?
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows
god evening sir i am studying m.sc(tech)electronics &instrumention.am i elegible to all industies
Why 4-20 amps is being used in instruments? Why cant we use any other range instead of 4-20 amps? Why only 4 amps is taken as lower limit and why 20 amps is taken as the higher limit?
Draw a group of instruments interlocked to a Pump & Motor?
How can measure flow in oil line?which type of transmitter is generally used?
What is mean by analytical instrumentation?
What should be the main consideration while starting the Rotating compressor when we dont know the cut in and the cut off pressure setting of the pressure switch
What is the constant voltage unit?
How d.p. Transmitter can be applied to close tank?
Give 2 application of quartz crystal used for process parameter measurement.
What is standard procedure of manual mapping in Radar type level transmitter?
How INtools is useful for routine Instrument maintenance?
Where Can i take a SPI INtools training in Mumbai? In Rolta India Ltd to whom I should approach regarding of SPI INtools Training?
need instrumentation job completed 1 year trainee ship in mnc pesticide company. now in search of job