how we are measuring the winding temperature of the
transformer?
Answer Posted / sripellirajukumar
hi this is rajukumar
transformer testing engineer
actually in power transformer we will be using one sensor
that is WTA ..windidng temperature indicator..by that device
we can check the winding temperature of transformer.. when
the fault occures the winding temperature much be rised....
at that fault time this WTA will sence the obnormal
temperature of winding then it will send trip signal to the
ckt breaker...
but in heat run test we can not find the winding temperature
..but we can find how much the transfomer is heating on full
load current...
thanks..
| Is This Answer Correct ? | 18 Yes | 12 No |
Post New Answer View All Answers
How energy is generated in hydroelectric power plant?
Can we use shunt trip coil instead of trip coil with protection relay for protection?
why r we using shell transformer for low voltage
What is transient Phenomenon?
how to select proper cable for ct wiring so that drop within the limit.
What happens to a motor if it is connected in Delta connection
Differentiate between ideal and non ideal current sources?
What is conventional thermal current (Ith)
What are the Full Forms of TVM, MTL, CVT ?
What is the polarization index value ? (Pi value)and simple definition of polarization index ?
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
What is the formula for selecting the cabels according to load? How to calculate what sq.mm cabel to be used?
what are the possible reaons & remedies if resistance of NGR getting heat up
whit is 33kv power 300*300 cable full current with formula
Define active and passive network?