What is meant by the KA-rating of a circuit breaker? In
this regard, discuss the stresses experienced by the
circuit breakers
Answer Posted / anand
KA Rating of Circuit Breaker is nothing but a Short Circuit
Breaking Current Capacity of Circuit Breakers which is
around 40 KA EHV Circuit Breaker.
The Circuit Breakers do experience Mechanical Stresses
during closing & opening operations.
| Is This Answer Correct ? | 28 Yes | 5 No |
Post New Answer View All Answers
What information we need to prepare relay coordination chart
describe the fully control circuit diagram of ac drives
Is it possible to measure the voltage of a battery from a single terminal?
Grid fault level [KA]?
How many Zones can be in Conventional type fire alarm system & how can we detect the fire in Conv. type FAS?
What is value of earth resistance required for substation and equipment earthing and what are the reference guidelines
Why lose 1 phase voltage in 33kv to 415v stepdown transformer
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
the site measured knee point voltage of protection class CTs should be greater than rated knee point voltage? what about meetering class CTs. Should it be below the rated knee point voltage?
What is the difference between PLC and Embeded system
what is arc flash and what are the hazards involved
What is the maximum number of swithes that can be connected in series up to down stream point in an LV Distribution system?
What is the accepted limit to increase the choosen transformer capacity over the load and why ?
The size and construction of bushings in a transformer depend upon?
Earth leakage relay basic knowledge principle