What is mean CT Saturation? How to calculate?
Answer Posted / rishit
Sorry to say Mr Kiran Patil if CT is shorted ckted then it
will complete the ckt and save it from any further damage
and meter connected to that CT not able to read current
flowing from that CT.
There are two simple way to calculate the CT saturation
1. There is an instrument operates on 240v,50HZ known as RED
PHASE instrument it is an Australian instrument.
2. Primary injection method in this method we use an
instrument which can only provide current to both of the
primary position of the CT known as P1,P2 and secondary of
that CT are being short ckted so as to calculate the current
and with the help of tong tester we can calculate the
secondary current.
for example we are having CT ratio of 10/5 A and we are
providing primary current of 10 A and from secondary point
we are calculating 5 A current then CT are OK but if we are
getting lesser current than we must say that CT are saturated.
| Is This Answer Correct ? | 17 Yes | 50 No |
Post New Answer View All Answers
How do you calculate the actual power consumption of an inductive load appliance. Say, a deep freezer of 200watts
Explain Creepage Distance of Insulator
What is distance between electrical panel to land ?
my question is how to answer the question "you are from b.tech eee background and why do you want to go for banking
what is cathodic protaction?
How to measure power in 2 or 4 or n phase circuit? Please give me a formula.
Advantages of using generator circuit breaker (GCB) scheme in a power station ?
what is the problem when i want to close a circuit breaker by local position it closes well.but when i close it in remote position it trips
what is the breaking capacity and making capacity of circuit breaker and how
How to test REF relay testing for LV panel as per Kahramaa standard?
what is a types of short circuit and what is a types of distance protection tests
Define corner frequency?
relation between power station capacity and voltage level?
Please tell me in DETAIL about the following 3 types of fuses or recommend me a good power system protection book or a website link ? 1.Dropout Fuse 2.Striker Fuse 3.Empulsive fuse (not sure if its impulsive or explosion fuse , sorry)
How cable from Kit-Kat to main switch, from starter to motor are designed?