WHAT IS THE SIGNIFICANCE OF VECTOR GROUPS IN TRANSFORMER?
WHAT WILL BE EFFECT WHEN PHASE DISPLACEMENT CHANGES IN
TRANSFORMER?
Answer Posted / poonam
Vector Groups are made especially to make out difference in
the connections. The connection can be delta(D) or star(Y)
The number after that indicates the phase difference
between the primary and the secondary voltage.
e.g.-> Y11 means transformer is star connected with
secondary voltage leading the primary voltage by 30 degrees.
I am not sure of the effect of phase displacement in
transformer
| Is This Answer Correct ? | 16 Yes | 12 No |
Post New Answer View All Answers
what happen as when voltage drop(or may decrease) ? in case of atomic base theory?
what is the difference b/w UHVDC and HVDC(LIGHT)?
in what type of applications v can use q meter?
If I want to connect a capacitor bank on the HT side of a 11kV/415V, 3 phase delta-star distribution transformer to supply Reactive power to it..what practical specifications of a Capacitor bank that can i've??please reply..
If we use 250A MCCB as a incomer in Control panel for a fault level of 50kA for one second ,assuming temperature rise from 85 Deg. to 100 Deg , Then what will be the Aluminium Bus-bar size for 250A MCCB? Explain in detail.
What is mean by hot and cold loop testing?
what is active power & reactive power?
WHAT IS SUBSTATION & ACCORDING TO VOLTAGE HT,EHT SUBSTATION EXPLAIN IT
we have 3.5MVA-11/6KV transformer. how can we calculate earth fault current and NGR calculation?
What is VSCF windelectrical system?
difrent between vcb acb sf6 and mccb breakers
what is auto re-closer?
How we calculate the Multiplying Factor of Kwh meter for 3 phase alternator.
What is the function of interposing current transformer?
how to calculate current and voltage in a same circuit?