Answer Posted / joseph
Calculating Power Factor at LT or HT side is the same, as
P.F. is simply the ratio between the Active Power and
Apparent Power. Hence, if you have got both these
parameters then just divide Active Power by Apparent Power
(kW/KVA or MW/MVA as the case may be.)
| Is This Answer Correct ? | 26 Yes | 2 No |
Post New Answer View All Answers
what is the ckt diagram of a tubelight and is it the simplest ckt of electrical engineering and also the component?
what is the effect of power factor of machines in starting current
what percent do you derate your copper wire when you change from copper buss to copper wire
Dear all i want to know SEWA Electrical Supervisor Licence test Previous Year Questions ? If any body know please send to me zohairaukllah@yahoo.com
Connection diagram for KW meter and Kva meter
what is the correct method for the outdoor termination of 19/33 KV HT cable step by step?
What is vaccum currcuit breaker.define with cause and where be use it device?
What is given by the definition in BIL IMP/PF = 950/395 kV. This was found in a name plate of a power transformer.
How to calculate Temp from Resister from PT100 equation,
Can the output voltage of a rectifier be greater than the input AC voltage without the use of any voltage multiplier in the circuit??please provide the explanation too..
can I improve the furnace power factor (10 mva transformer) by adding a capacitor bank before the transformer.Does system power factor vary a lot with the furnace PF?
What is resonant peak?
What will be the voltage impact on secondary side of two transformers with different vector groups when both voltages are compared.
The Howland current source produces a A Unidirectional floating load current B Bidirectional single-ended load current C Unidirectional single-ended load current D Bidirectional floating load current
why in the three pin plug all 3 pins are cutted ?