What is the Difference Between MCCB & ACB & VCB
Answer Posted / kumar t
Mccb is moulded case circuit breaker.
ACB is air circuit breaker.
VCB is vacuum circuit breaker.
MCB is stand for miniture circuit breaker.It is for low
voltages.
MCCB is stand for moulded case circuit breaker. It is for
medium voltages.
ACB is stand for Air circuit breaker.It is for high
voltages.
| Is This Answer Correct ? | 66 Yes | 123 No |
Post New Answer View All Answers
How to test REF relay testing for LV panel as per Kahramaa standard?
i have faced a problem in ro plant grunfos make bm30type pump it is 22kw pump. We start this pump using siemens 3rw 4423-ibc44, 30kw softstarter but this soft starter will frequently failier so we planed to change dol starter. So pls tell anybudy its possible or not.
Transformer how to maintaince a check b check c check d check
what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm
Cables Construction hi friends, 0.6/1/1.2 kV LV , DC and Control cables are concentric copper conductor what does its means and what is the use of concentric copper conductor,and are this with copper tape shield or copper screening, ? thanks
how to control the speed to switched reluctance motor
What technology is used in latest generators?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING) I O (current operating)?
What are merits & De-merits of State-Space Method? What is series programming, parallel programming, general programming & direct programming ? And, difference between these programmings Techniques ?
what is the difference between elcb and rccb ?
what is the current density of copper & alluminium.
How to calculate the sag of OPGW during stringing???
You are of electrical field and you are going for software? Why
What is corkscrew rule?
working function importance of mdc meter