Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

a 3 phase motor was running with delta connected, suddenly
one phase winding got burnt off, what will be the effect ?

Answer Posted / rvg

delta connected winding, one winding burnt off means, its
open circuited. So the motor will work as open delta system
and run normaly with non uniform torque.
The max. load that can carry will be reduced to 57.7% of
full load.
If the motor is connected through a phase faliure relay,
the relay will trip the total ckt.

Is This Answer Correct ?    111 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Single line diagrams for star to delta and DOL starters.

2261


how to setting Load amps tripping time and extra settings for load Transformer protection relay with RMU panel using C&S model relay..?

1128


How is the connection of the tap changer on the HV side been made?

1966


The specific heats of the gas at constant pressure and constant volume are respectively 1.0 kJ/kg K and 0.72 kJ/kg K; the value of R for the gas is

1136


where is the need for short circuit test for 3 see is required and why? can you explain in brief with application

1949


Why we specify TNC switch with 1NO 1NC ,2NO 2NC ? how we get connection.?

1769


what do u understand about FACTS? how they are useful?

1980


what is the basic construction diffrance between servo motor ans sqiralcage induction motor

2461


what is the ms flat constant for calculating earth mat design calculation?

2503


how you taken aotitude test

2479


is there any lightning by passer is arranged in ship like buildings?

1932


Earth leakage relay basic knowledge principle

2173


Explain how you intend to work under pressure to meet up with deadline target?

2385


what is upper impedance and lower impedance of a distance relay

2035


What is the reason behind current flow(20 A) in amain earth cable of an SMDB? Is cuurent flow(45A etc) through a neutral cable acceptable?

1977