what is the function of a starter in a motor?
explain RLC circuit.
Answer Posted / nimish
The function of starter is to reduce the starting current
by inserting initially high resistance. In RLC series
circuit Resistance, inductance and capacitance are
connected in series. If XL is greater than XC then power
factor of circuit is Lagging and if XL is less than XC
power factor is leading. and if XL=Xc then power factor is
unity and this condition is known as resonance.
| Is This Answer Correct ? | 76 Yes | 28 No |
Post New Answer View All Answers
what is Fault level? why it is calculated? how will u decide same for our plant?
Define damping ratio.
HOW MANY TYPES OF FUSE?
Why an ac systems are preferred over dc systems?
Could the power factor on electrical system can affect the registration of the kwhr meter or the CT/PT?
Explain the working of variable frequency transformer?
how to check ac servo motor
DG Earth Value?
What is meant by harmonic distortion?
What is hipot test procedure?
I am having a 42KW 3 phase electrical heating furnace, heating element is 80/20 nichrome material, my connections is made in such a way that 2 star connection compromising 2 coils per phase so totally 12 coils, shall if i use it unbalanced star condition (instead of 2 group of 3 phase or 1 group of 3 phase, connecting 4 phases of 5 phases) what will be the consequences and is it acceptable?
EXPLAIN USE OF ROCKING ARRANGEMENT IN ELECTRIC HEATING?
How to calculate earth fault current for 6.6 KV , 50 HZ , 756 Amps , 3000 RPM , 0.8 PF generator
HI....HOW CAN BE MESARED THE VALVE OF NEUTRAL GROUND RESISTOR WHIC IS LOCATED AT SWICHGEAR ON GENERATOR SIDE....
May I know how much values to be set for earth fault, over current and short circuit values at 11kv side? I have 11kv van 1250amps rating. Present it's taking load 80amps?