What is the power ratio between power in Star and Delta
circuit?
Answer Posted / priyadharsini
power = 3vicos
in delta Iphase = Iline/rt3.
Vphase = Vline
ie in delta connected ckt P= rt3VphaseIphasecos
IIly in star connected vphase=Vline/rt3,
Iline=Iphase
ie Power = rt3 vpahseIphaseCos
ie. in both star and delta power remain same
therefore the Power ratio = 1.
| Is This Answer Correct ? | 25 Yes | 26 No |
Post New Answer View All Answers
What is touch potential and step potential?
what is auto re-closer?
Why we use Electrical energy rather than any other type of energy, mostly? Explain behavior of open secondary CT and short circuited secondary PT in energized condition?
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
How many turns are there in primary winding? (In Transformer)
when we decide to use soft starter drive or vfd drive in mcc to operate apump?
List some examples of renewable energy?
What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?
why the neutral line is not giving shock to us if we touch it ?
HOW TO CALCULATE THE VT SIZING?
A 3 phase transformer's (Y-Y) Y and B phase is (Y and B connection not broken) broken from neutral and R and Nutral connection is ok, what will be the relay tripping and why
why the projects getting loss?
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
how to calculation increase power factor for single phase
which protection used in power plant?