For 11KV Vaccum Circuit Breakers(VCB) are suitable to use.
Now-a-days SF6 (Sulphor Hexa Fluoride) breakers are
available but VCBs are economical than SF6 breakers.
For 33KV - both VCB & SF6 breakers can be used,but SF6
breakers are safer than VCBs. VCBs are more economical
For 66KV - SF6 breakers are the best to use
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / birinchi narayan boruah
For LT: 415 V
Use ACB (Air blast Circuit Breaker)
For 11KV and 33KV:
Use VCB (Vaccum Circuit Breaker) or SF6 CB (Sulphar Hexa Floride Circuit Breaker).
For 66KV, 132KV and 220KV:
use SF6 Circuit Breaker or Oil Circuit Breaker
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / nikhil panchal
Below 15kV AIR CB
22 to 66 kV VCB
115-230 kV SF6
UPTO 765kv ABCB
Is This Answer Correct ? | 4 Yes | 1 No |
below 36kV, it is better to use VCB, and above 36kV to use SF6
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jegan.j
11kv - vcb (vaccume circuit breaker)
mccb(moulted case circuit breaker)
mcb(maniature circuit breaker)
acb(air circuit breaker)
33kv - sf6
66kv - sf6
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / fazil pasha
For 11KV Vaccum Circuit Breakers(VCB) are suitable to use.
Now-a-days SF6 (Sulphor Hexa Fluoride) breakers are
available but VCBs are economical than SF6 breakers.
For 33KV - both VCB & SF6 breakers can be used,but SF6
breakers are safer than VCBs. VCBs are more economical
For 66KV - SF6 breakers are the best to use
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manoj
upto 11kv air break or oil break type.
between 11kv to 66kv mainly oil CB.
between 132kv to 275kv is shared by oil and gas blast CB.
between 400kv and above gas blast(SF6)type.
Is This Answer Correct ? | 2 Yes | 3 No |
What should be distance required in between two phase of HT cionductors in open area??????
What is load curve?
What is the use of lag compensator?
for 8 mva 33/11 kv transformer what will be the setting of differential relay on which it trip & what is the HF setting in this relay
What is the types of HT motor testing
11KV AND 22KV NETWORK KW CAPACITY IN RING AND RADIAL?
what do you mean by cl PS CTs? What are technical details required for it's manufacturing?
What is the distance between body earthing and neutral earthing.?
What is PMG and AREP excitation system in generator
wat is the importance of reactive power in power generation.....if it is zero means wat will happen to system........
1)What will be full load current for 1000kva 3 phase generator. 2)What will be full load current for 20Kva 1 phase inverter.
what is the actual difference betwen constructional details and constructional features?