what is puling in n pulling out in flame scanner system?
Answer / bala
Flame Scnner Basic function- viewing flame in furnace
It has provided in order to avoid unwante boiler trip
Pull in / pull out manual set value from 0 - 100 %
pull in always higher than pull out eg- 40 % & pull out 20 %
when initial flame exceed above 40 % it will consider as
flame
when flame drop drop from 40 - 20 it will consider as flame
when drop below 20 % it will take as no flame signal
the o/p contact flame / noflame will be taken for boiler
safty operation
| Is This Answer Correct ? | 6 Yes | 0 No |
Will Intergraph support SmartPlant Instrumentation in an AutoCAD or MicroStation environment on a long-term basis?
How to calculate flow of air bubbler type level transmiter According hight and density
2 Answers Qatar Petroleums, RKS,
How to measure density of oil in your kitchen. i.e indirectly to verify the quality of oil using min. gadgets available in the kitchen/house.
Explain the combusion chamber
How to calibrate level transmitter with use of HART?
why the derivative in PID is always set to zero?
how to measure temperature from resistance of rtd?and how to measure temp from voltage of thermocouple?is there any formulas?
What is cavitation. what is the effect of it on control valve and how is it prevented.
explain the working of Coriolis Flowmeter.
What is Cu-100 and Cu-1000 ? and tell me its application ?
what is the zero elevation and zero supresstion in level measurement, how can use it?
what is isolation Transformer???...
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)