What is OLTC in a transformer, specify its fuction.
Answer Posted / sriman
OLTC MEANS ON LOAD TAP CHANGER
THE FUNCTION OF OLTC IS TO CHANGE THE VOLTAGE LEVEL OF
SECONDARY SIDE OF TRANSFORMER ACCORDING TO CHANGE IN LOAD
TO MEET THE REQUIREMENT AND TO KEEP THE VOLTAGE CONSTANT
WITHIN THE LIMITS
Is This Answer Correct ? | 517 Yes | 41 No |
Post New Answer View All Answers
what is the formula of starting current of 3phase and 1 phase motor???
what is the diff. between x'mer , isolation x'mer & ultra-isolation x'mer ?????????????
What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?
what should be correct gas pressures to be a 1.5 ac unite
Some times to change of DOR of a motor, interchange of R & B is not effected and RYB take same current, but interchange of R&Y is effected ie change the DOR. My doubt is what is the problem in motor and how it is happen.
why do we use 25kv supply for traction purpose?
which stabilizer is better ? AVR, Servo Stabilizer, Static stabilizer etc & why explain it
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
How many kw will suply from one db
What si the d/f b/w KVA & KWH, kvarh & kvar, kwh & kvar phase voltage & line voltage
if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.
What is the theoretical reason for the size of a zig zag grounding transformer to be 1.732 times less than that of a wye-delta grounding transformer used for the same application?
What is the formuala to calculate the rating of motor protection circuit breaker
is it possible to say motor horsepower number without seeing name plate(when name plate damaged)
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables