the distance from my office to d.g is aprox 400mtrs and
voltage drops ibn my office near about 40 volt what should
i do p[ls suggest.
Answers were Sorted based on User's Feedback
Answer / sabale.dnyanehswar@gmail.com
IF U ASKING ABT DC Voltage then ans is
1. u have to increase the sq.mm size of the cable. i.e if
u r laid cable size is 16 sq.mm. u can go to 25 sq.mm.
2. u have to increase u r battery Amphour rating . by
replacing it with higher rating.
if u asking abt AC voltage:
1. check the DG set terminal voltage if voltage is not
proper then check at AVR terminal. if there also not ok.
then check it with another AVR card.
2. if AVR is OK then check any leakage of cable with taking
megger & continuty with earth.
3. if problem is found in cable then replace with new one
or increase the rating of cable.
if everythink is ok. then take voltage at receiver end with
out load. one by one increase the load at every time
voltage reading. if found prob. in another ckt. rectify it.
The range should be +- 5% should be accepted.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thowsif
Hi ,
Go through this link:-http://www.psihq.com/iread/faqvolt.htm
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amit chaudhary
You should check the cable size which you are using from
your office to DG set. May it will need to increase the size
of cable.
If you are not using this DG set for another purpose then
you can increase the generator voltage by AVR to get the
suitable voltage in your office.
If the cable is heated during the load then you will have to
increase the cable size.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj
Above all answers are right but one more we can do is to
add capacitor at load end to increase the voltage.
Is This Answer Correct ? | 0 Yes | 0 No |
Why Transformer in KVA?
41 Answers APCPDCL, Apollo Power, College School Exams Tests, Electrical Tech, Hitech, HP, L&T, MDL, Oil and Gas Jobs, TATA,
what is the use of spherical metal balls attached on to the earth wire of transmission over head lines?
what will happen if phases are not shorted with neutral in transformer impedance test? and if neutral is not connected with ground?
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
what is F.A.P in fire alarming system?
With a phasor diagram show the effect of increasing the field current of a generator supplying a constant real power and connected to a grid system.
When a square wave is applied to primary of a transformer then what will be output wave form of secondary ?
Why the isolation treasforfer are connected at out put of the ups ig 200kva ??????????????????
tate and explain super position theorem
role of europe union in UK safety legistlation (electrical safety)
DEAR SIR, HOW TO CALCULATE WELDING TRANSFORMER CAPACITY IN KW OR KVA (POWER). TWO WELDING TRANSFORMER USED WHAT TYPE OF DG SET CAPACITY LIKE ( 45 KVA OR 62.5 KVA), PLEASE TELL THE WELDING TRANSFORMER RATEINGS. I AM REFINARY (TANKS WELDING) THANKING YOU
Sir pl provide 5 year sample paper for post junior engineer(electrical).I have currently applied for junior engineer (electrical) on RRB Ajmer