ALLInterview.com :: Home Page      
 Advertise your Business Here     
Browse  |   Placement Papers  |   Company  |   Code Snippets  |   Certifications  |   Visa Questions
Post Question  |   Post Answer  |   My Panel  |   Search  |   Articles  |   Topics  |   Errors
   Refer this Site  Refer This Site to Your Friends  Site Map  Contact Us      
   
 
Categories >> Engineering >> Electrical Engineering
 


 

 
Question
How to calculate the current carrying capacity of 
electrical cables
 Question Submitted By :: Electrical Engineering
  I also faced this Question!!      
Answer Posted By  
 Answers were Sorted based on User's Feedback
Answer
# 1
Current carrying capacity = FLC / DF
To refer cable catelouge choose the cable sizes
-Derating factor (DF) =0.72
-Full load current (I)= P / (1.732 x V x P.F) 

Is This Answer Correct ?    77 Yes 28 No
syed rafiudeen
 
Answer
# 2
current carrying capacity of the conductor is depend on
size of cable and current density of used material of cable
conductor

current carring capacity= size of conductor/current density
of materils 

Is This Answer Correct ?    78 Yes 30 No
ghanshyam kannaujiya
 
 
Answer
# 3
For calculate the current carrying capacity.
First we should calculate the cross section area of the
conductor (sq.mm) and conductor material used in cable.

Each and every matals are having its own current carring
capacity. This table is avail at IS.

Current carring capacity may reduce by some other factors
like the cable length and insulation's heat withstandable
capacity. 

Is This Answer Correct ?    61 Yes 14 No
venkatesh a
 
Answer
# 4
There is no need to calculate ampacity of the cable it would
be provided by the manufacturer its self or else if you want
to calculate it by your self you should also know its
specific resistivity,working temp,core dia & insulation
thickness. 

Is This Answer Correct ?    115 Yes 71 No
lokesh.thota
 
Answer
# 5
The current carrying capacity of a cable is called
Ampacity. For the porpose of the above calculation there
are some concepts that must be taken in consideration .
like Dia,Insulation material and thickness,type of conductor
(Copper/Aluminium),Resistivity and the working conditions.
For BETTER CONCEPT I advice the readors to please refer
the "Recommended Cable Sizes and their load capacity as per
IS:13947 & IEC 60947". Below given table can help you.
Rating Cu Al
10A 1.5MM2 1.5MM2
15A 2.5MM2 2.5MM2
20A 2.5MM2 4.0MM2
25A 4MM2 6MM2 

Is This Answer Correct ?    61 Yes 23 No
dipesh kumar
 
Answer
# 6
Actually current carrying capacity of the cable we can from
the manufacturer, But for the referance purpose I can give
some idea about current capacity of the cable.
So generally we are using two types of cable i.e,. copper &
Aluminium.
copper is the best conductor than the aluminium
At 1Sqmm copper conductor will Approx 2 amp in ground
At 1Sqmm copper conductor will Approx 2.4 amp in air
At 1Sqmm Aluminium conductor will Approx 1.2 amp in ground
At 1Sqmm Aluminium conductor will Approx 1.6 amp in air.

For example:
p=50kw
load current=87amps
So
for aluminum cable size(air)= load current/1.6
=87/1.2
=72.5
But In the market there is no availability for 72.5 Sqmm so
we can propose 70Sqmm or 95Sqmm.
This is the one of the best procedure for for cable
selection with using catelogues 

Is This Answer Correct ?    56 Yes 25 No
t.raju goud
 
Answer
# 7
It depends on many factors.

1. Material - Copper/ Aluminum
2. Voltage Class - Some volts to 765 KV
3. AC/ DC
4. Type of Insulation
5. Most Importantly - Cable Cross-section Area

Refer IEC-60183 for detailed guide 

Is This Answer Correct ?    40 Yes 12 No
arun reddy
 
Answer
# 8
Refer IEC 287.If you want me to calculate the same. i will
do it for you 

Is This Answer Correct ?    28 Yes 17 No
amit jain
 
Answer
# 9
Well, First try to calculate the total load of the system.
For example total load is 1000KW. The current can be
calculated as P=1.732VICOS(PHI). Hence total current will
be 1732A by considering V=415volt, power factor=0.8.

Step2: To calculate the cable size

Vd = mV/L/A

where Vd= Allowable voltage drop which is normally 2.5
percentage to 4 percent.
L = Lenght of the cable from the source to feeder
A = Ampere rating

Let us consider L = 1000Meters
A = 1732A
Vd = 2.5 percentage of 415V as in U.A.E.
= 2.5*415/100 = 10.375

Use these value in the above formula

mV= Vd/L*A
= 10.375/1000*1732
= 0.005 volt

Refer to the cable catalogue in your region and find out
the current carrying capacity of the cable which will be
totally depend upon the atmospheric condition, in cold
place a smaller diameter of cable can carry larger current
and in hot areas the same size will carry lesser current.

In U.A.E. we are normally using 11x1c 630sqmm cable with
2500A incomer breaker. But cross check the voltage drop as
calculated above is within the limit of voltage drop of
these cables else you have to go to higher size of cable
untill the voltage drop met the design milli volt drop of
the cable. 

Is This Answer Correct ?    8 Yes 5 No
abdul haseeb khattal
 
Answer
# 10
hi frnd.. what will u say for the given ques. if interviewer asked, How a manufacturer determines the current carrying capacity of electrical cables?? 

Is This Answer Correct ?    2 Yes 0 No
himanshu
 

 
 
 
Other Electrical Engineering Interview Questions
 
  Question Asked @ Answers
 
WHAT ARE THE DATAS REQUIRED FOR SCS SIGNAL LIST PREPARATION? l&t 1
what is the function of fire alarm system?   5
what is dyn 11   3
some meggers have three terminals. wat is the real function of the earth terminal?   2
Why the steam turbines are run at high speed where as the hydro turbines are run at low speed?   1
what is meant by frequency ? tcs 10
why dc did not flows to earth?   1
what power factor should we maintain to get maximum benefits our organisation load is 10 MW? is it best to maintain the PF at .96 rather than Unity to save electricity bill?   1
Am i eligible to get electrical supervisor licence? As i did diploma as well as degree in Electrical Engg. in June 2011. Now i am working in 15 MW Power plant from 2 mnths. i belongs to Maharashtra.   1
What will hapen if we run generator below 47.6hz frequency? tata 9
what is the different beetween kva and kwh?   4
what is the internal fuction of a ceiling fan?   2
 
For more Electrical Engineering Interview Questions Click Here