ALLInterview.com :: Home Page            
 Advertise your Business Here     
Browse  |   Placement Papers  |   Company  |   Code Snippets  |   Certifications  |   Visa Questions
Post Question  |   Post Answer  |   My Panel  |   Search  |   Articles  |   Topics  |   ERRORS new
   Refer this Site  Refer This Site to Your Friends  Site Map  Bookmark this Site  Set it as your HomePage  Contact Us     Login  |  Sign Up                      
Google
   
 
Categories >> Engineering >> Electrical Engineering
 
 


 

 
 Civil Engineering interview questions  Civil Engineering Interview Questions (3078)
 Mechanical Engineering interview questions  Mechanical Engineering Interview Questions (3289)
 Electrical Engineering interview questions  Electrical Engineering Interview Questions (13332)
 Electronics Communications interview questions  Electronics Communications Interview Questions (2363)
 Chemical Engineering interview questions  Chemical Engineering Interview Questions (416)
 Aeronautical Engineering interview questions  Aeronautical Engineering Interview Questions (77)
 Bio Engineering interview questions  Bio Engineering Interview Questions (17)
 Metallurgy interview questions  Metallurgy Interview Questions (79)
 Industrial Engineering interview questions  Industrial Engineering Interview Questions (163)
 Instrumentation interview questions  Instrumentation Interview Questions (2381)
 Automobile Engineering interview questions  Automobile Engineering Interview Questions (106)
 Mechatronics Engineering interview questions  Mechatronics Engineering Interview Questions (38)
 Marine Engineering interview questions  Marine Engineering Interview Questions (44)
 Power Plant Engineering interview questions  Power Plant Engineering Interview Questions (77)
 Engineering AllOther interview questions  Engineering AllOther Interview Questions (1196)
Question
How to calculate the current carrying capacity of 
electrical cables
 Question Submitted By :: Electrical-Engineering
I also faced this Question!!     Answer Posted By  
 
Answer
# 1
current carrying capacity of the conductor is depend on
size of cable and current density of used material of cable
conductor

current carring capacity= size of conductor/current density
of materils
 
Is This Answer Correct ?    77 Yes 29 No
Ghanshyam Kannaujiya
 
Answer
# 2
There is no need to calculate ampacity of the cable it would
be provided by the manufacturer its self or else if you want
to calculate it by your self you should also know its
specific resistivity,working temp,core dia & insulation
thickness.
 
Is This Answer Correct ?    115 Yes 68 No
Lokesh.thota
 
 
 
Answer
# 3
Current carrying capacity = FLC / DF
To refer cable catelouge choose the cable sizes
-Derating factor (DF) =0.72
-Full load current (I)= P / (1.732 x V x P.F)
 
Is This Answer Correct ?    73 Yes 26 No
Syed Rafiudeen
 
Answer
# 4
For calculate the current carrying capacity.
First we should calculate the cross section area of the
conductor (sq.mm) and conductor material used in cable.

Each and every matals are having its own current carring
capacity. This table is avail at IS.

Current carring capacity may reduce by some other factors
like the cable length and insulation's heat withstandable
capacity.
 
Is This Answer Correct ?    60 Yes 14 No
Venkatesh A
 
Answer
# 5
The current carrying capacity of a cable is called
Ampacity. For the porpose of the above calculation there
are some concepts that must be taken in consideration .
like Dia,Insulation material and thickness,type of conductor
(Copper/Aluminium),Resistivity and the working conditions.
For BETTER CONCEPT I advice the readors to please refer
the "Recommended Cable Sizes and their load capacity as per
IS:13947 & IEC 60947". Below given table can help you.
Rating Cu Al
10A 1.5MM2 1.5MM2
15A 2.5MM2 2.5MM2
20A 2.5MM2 4.0MM2
25A 4MM2 6MM2
 
Is This Answer Correct ?    58 Yes 23 No
Dipesh Kumar
 
Answer
# 6
Actually current carrying capacity of the cable we can from
the manufacturer, But for the referance purpose I can give
some idea about current capacity of the cable.
So generally we are using two types of cable i.e,. copper &
Aluminium.
copper is the best conductor than the aluminium
At 1Sqmm copper conductor will Approx 2 amp in ground
At 1Sqmm copper conductor will Approx 2.4 amp in air
At 1Sqmm Aluminium conductor will Approx 1.2 amp in ground
At 1Sqmm Aluminium conductor will Approx 1.6 amp in air.

For example:
p=50kw
load current=87amps
So
for aluminum cable size(air)= load current/1.6
=87/1.2
=72.5
But In the market there is no availability for 72.5 Sqmm so
we can propose 70Sqmm or 95Sqmm.
This is the one of the best procedure for for cable
selection with using catelogues
 
Is This Answer Correct ?    54 Yes 25 No
T.raju Goud
 
Answer
# 7
It depends on many factors.

1. Material - Copper/ Aluminum
2. Voltage Class - Some volts to 765 KV
3. AC/ DC
4. Type of Insulation
5. Most Importantly - Cable Cross-section Area

Refer IEC-60183 for detailed guide
 
Is This Answer Correct ?    38 Yes 12 No
Arun Reddy
 
Answer
# 8
Refer IEC 287.If you want me to calculate the same. i will
do it for you
 
Is This Answer Correct ?    25 Yes 17 No
Amit Jain
 
Answer
# 9
Well, First try to calculate the total load of the system.
For example total load is 1000KW. The current can be
calculated as P=1.732VICOS(PHI). Hence total current will
be 1732A by considering V=415volt, power factor=0.8.

Step2: To calculate the cable size

Vd = mV/L/A

where Vd= Allowable voltage drop which is normally 2.5
percentage to 4 percent.
L = Lenght of the cable from the source to feeder
A = Ampere rating

Let us consider L = 1000Meters
A = 1732A
Vd = 2.5 percentage of 415V as in U.A.E.
= 2.5*415/100 = 10.375

Use these value in the above formula

mV= Vd/L*A
= 10.375/1000*1732
= 0.005 volt

Refer to the cable catalogue in your region and find out
the current carrying capacity of the cable which will be
totally depend upon the atmospheric condition, in cold
place a smaller diameter of cable can carry larger current
and in hot areas the same size will carry lesser current.

In U.A.E. we are normally using 11x1c 630sqmm cable with
2500A incomer breaker. But cross check the voltage drop as
calculated above is within the limit of voltage drop of
these cables else you have to go to higher size of cable
untill the voltage drop met the design milli volt drop of
the cable.
 
Is This Answer Correct ?    6 Yes 5 No
Abdul Haseeb Khattal
 
Answer
# 10
hi frnd.. what will u say for the given ques. if interviewer asked, How a manufacturer determines the current carrying capacity of electrical cables?? 
Is This Answer Correct ?    1 Yes 0 No
Himanshu
 

 
 
 
Other Electrical Engineering Interview Questions
 
  Question Asked @ Answers
 
Why Closing coli supervision is not required for Circuit breaker. JSW 1
what are the causes for strip heater failure ?   1
why dc did not flows to earth?   1
I want to know what must the CT ratio be on a load of 300A is a 3PH nutral to earh installation?   4
if dc motor can operate by ac supply ? if its possible means how ?   2
Please specify the parts of VCB&ACB   1
why transformer fuse wire is very thin as compared to home fuse wire while voltage lavel is low   1
140 is load amps for a equipments and what ratio of CT requied for installimg ammeter to amps montering purpose?   1
what is the size of ht cable of 33kv ht line and transformers ratings are 2.5mva and 5.5mva.please send formula also.   1
Name the earthings? HSL 3
if 20 hp motor starts directly delta connection.motor what will be the effect. HP 3
tell me about sf6 breakers   4
 