ALLInterview.com :: Home Page            
 Advertise your Business Here     
Browse  |   Placement Papers  |   Company  |   Code Snippets  |   Certifications  |   Visa Questions
Post Question  |   Post Answer  |   My Panel  |   Search  |   Articles  |   Topics  |   ERRORS new
   Refer this Site  Refer This Site to Your Friends  Site Map  Bookmark this Site  Set it as your HomePage  Contact Us     Login  |  Sign Up                      
tip   To Refer this Site to Your Friends   Click Here
Google
   
 
Categories  >>  Engineering  >>  Electrical Engineering
 
 


 

 
 Civil Engineering interview questions  Civil Engineering Interview Questions
 Mechanical Engineering interview questions  Mechanical Engineering Interview Questions
 Electrical Engineering interview questions  Electrical Engineering Interview Questions
 Electronics Communications interview questions  Electronics Communications Interview Questions
 Chemical Engineering interview questions  Chemical Engineering Interview Questions
 Aeronautical Engineering interview questions  Aeronautical Engineering Interview Questions
 Bio Engineering interview questions  Bio Engineering Interview Questions
 Metallurgy interview questions  Metallurgy Interview Questions
 Industrial Engineering interview questions  Industrial Engineering Interview Questions
 Instrumentation interview questions  Instrumentation Interview Questions
 Automobile Engineering interview questions  Automobile Engineering Interview Questions
 Mechatronics Engineering interview questions  Mechatronics Engineering Interview Questions
 Marine Engineering interview questions  Marine Engineering Interview Questions
 Power Plant Engineering interview questions  Power Plant Engineering Interview Questions
 Engineering AllOther interview questions  Engineering AllOther Interview Questions
Question
How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation
 Question Submitted By :: Vinay
I also faced this Question!!     Rank Answer Posted By  
 
  Re: How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
Answer
# 1
3core-185 sq. mm

Calculation:-

Current at HT = (1500 x 1.4)/ (33*1.732)
 
Is This Answer Correct ?    106 Yes 68 No
Divay Chadha
 
  Re: How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
Answer
# 2
please slect your cable in 11kv py side how much current
check first after you slect your ht cable.
 
Is This Answer Correct ?    50 Yes 23 No
J.kesavan
 
 
 
  Re: How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
Answer
# 3
Assume PF of transformer is .8.
rating of transformer=1500kVA=1500X.8=1200kW
V=433(3phase)
So that maximum current-
I= P/V*PF
=1200*1000/1.732*433*.=1600A
So cable size required if copper cable
1mm=4amp= 400sqmm(by consedering all factors)
For aluminium cable
1mm=2.5A=640sqmm
 
Is This Answer Correct ?    42 Yes 66 No
Govind Bisht
 
  Re: How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
Answer
# 4
simple for 11kv
Amp in HT= kva*1000/ 1.732*11000

= size for 78 amp HT XLPE 3 core 95 mm2 higher side.
 
Is This Answer Correct ?    45 Yes 19 No
Neeraj Tyagi
 
  Re: How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
Answer
# 5
for 11kv side current = kva*1000/1.732*11000

= 78.73 amps
for 78.73 amps 3 core 25 sqmm cable is sufficient
 
Is This Answer Correct ?    18 Yes 50 No
M.jagadeeshwar
 
  Re: How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
Answer
# 6
Generally HT cable sizing is not done based on the full
load current of the equipment but based on the prospective
fault level. For a 11kV network, generally it shall not be
less than 150sqmm XLPE.

Fault level at 11kV(furnished by respective EB)=100 MVA(say)

Details on EB's fault level can be obtained from EB.

Therefore fault current= 100*1000/(SQRT(3)*11000)
= 5.25 kA

Short circuit current rating (for 3-sec duration)of HT 11kV
XLPE cables with Alu conductor is as below:
95 sqmm: 5.16 kA
120 sqmm: 6.51 kA
150 sqmm: 8.14 kA
 
Is This Answer Correct ?    43 Yes 14 No
S.srinivasan
 
  Re: How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
Answer
# 7
1500kVA X 0.8 PF = 1200Kw = 1200000W

P=RT3 V I COS fi

SO, P
I = -----------
RT3 x V x COSfi

1200000
I = -----------------
1.732x1100x0.8

= 79 A

Now take cable table and select the suitable xlpe cable.

Uday
 
Is This Answer Correct ?    22 Yes 21 No
Uday
 
  Re: How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
Answer
# 8
11kv----13 amps on primary side

1500 kva 1.4 = 2100 amps on secondary
 
Is This Answer Correct ?    22 Yes 10 No
Gb
 
  Re: How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
Answer
# 9
First calculate the current of primary side(HT) and derate the cable by atleast 0.7.
Eg:1500*1000/(1.732*11000)=78.73A
Current I after Derating =78.73/.7 =112A (0.7 if laid on the trays or value will vary if buried in the ground).
Cable equivalent to rating has to be selected.
Now Short circuit withstand capacity (sq. of I X t in sec) has to be checked from the cable catalogue.This value of cable should be higher then SC withstand capacity of the ground usually it is 50KA.it less go for next size and finalise.
 
Is This Answer Correct ?    12 Yes 10 No
Madhu Mohan
 

 
 
 
Other Electrical Engineering Interview Questions
 
  Question Asked @ Answers
 
what is total power generation in tamilnadu What are the methods used powerfactor improved? which place DC transmission line usde?  5
Wat is power factor exact meaning in terms of technical terms plz explain ?  4
what time should we set to come on star contacter in stardelta starter?and for what reason we hav to set such time delay range?  2
What is an infinite bus bar?  27
on what priciple transformer works on?  5
we all know that both the generator and motor are electromechanical conversion devices.....then why we rate motor in kw and generator in kva???? KSEB3
how to calclate fault level  2
when an induction motor runs on load.at that time if we reduce the supply voltage the current increases.But when it runs without load,if we reduce the supply voltage the current also reduced.why?.i checked it practically also. Birla1
If one lamp connect between two phases it will glow or not?  6
11 kv metering is done in my factory.Meter show PF 1.000 but kvarh lag&lead show 24&94 respectively & Avg.PF is .956 .? is what i do for inproove my PF to 1.000  3
what is the formula to find out how many amps generater takes running on full load.  3
hi i am aziz electrical associate engineer. i am faceing problem in acs800 vvvf drive.it is tripping wothout any alarm/fault.i cheaked all parameters and fault function of drive, all are correct as well as communication parameters.but still it is tripping (drive is tripping in running position not in starting)  1
 
For more Electrical Engineering Interview Questions Click Here 
 
 
 
 
 


   
Copyright Policy  |  Terms of Service  |  Help  |  Site Map 1  |  Articles  |  Site Map  |   Site Map  |  Contact Us interview questions urls   External Links 
   
Copyright © 2012  ALLInterview.com.  All Rights Reserved.

ALLInterview.com   ::  Forum9.com   ::  KalAajKal.com