ALLInterview.com :: Home Page            
 Advertise your Business Here     
Browse  |   Placement Papers  |   Company  |   Code Snippets  |   Certifications  |   Visa Questions
Post Question  |   Post Answer  |   My Panel  |   Search  |   Articles  |   Topics  |   ERRORS new
   Refer this Site  Refer This Site to Your Friends  Site Map  Bookmark this Site  Set it as your HomePage  Contact Us     Login  |  Sign Up                      
Google
   
 
Categories >> Engineering >> Electrical Engineering
 
 


 

 
 Civil Engineering interview questions  Civil Engineering Interview Questions (3120)
 Mechanical Engineering interview questions  Mechanical Engineering Interview Questions (3300)
 Electrical Engineering interview questions  Electrical Engineering Interview Questions (13434)
 Electronics Communications interview questions  Electronics Communications Interview Questions (2385)
 Chemical Engineering interview questions  Chemical Engineering Interview Questions (420)
 Aeronautical Engineering interview questions  Aeronautical Engineering Interview Questions (77)
 Bio Engineering interview questions  Bio Engineering Interview Questions (17)
 Metallurgy interview questions  Metallurgy Interview Questions (80)
 Industrial Engineering interview questions  Industrial Engineering Interview Questions (165)
 Instrumentation interview questions  Instrumentation Interview Questions (2398)
 Automobile Engineering interview questions  Automobile Engineering Interview Questions (107)
 Mechatronics Engineering interview questions  Mechatronics Engineering Interview Questions (38)
 Marine Engineering interview questions  Marine Engineering Interview Questions (45)
 Power Plant Engineering interview questions  Power Plant Engineering Interview Questions (80)
 Engineering AllOther interview questions  Engineering AllOther Interview Questions (1203)
Question
How do you select a cable size(Cu&Al) for a particular load
 Question Submitted By :: Electrical-Engineering
I also faced this Question!!     Answer Posted By  
 
Answer
# 1
While Calculating The Proper Size Of Cable You Should Know
The Full load current Also You Should Consider The Derating
Factor Of Cable , Cable Current rating varies according to
different types of Cable distribution ie where it above
ground or underground.
 
Is This Answer Correct ?    48 Yes 8 No
Ashish
 
Answer
# 2
Calculate the full load current(10% more).Choose prper
rating of Cu & Al. conductor from the chart.
 
Is This Answer Correct ?    43 Yes 19 No
Panda N.n
 
 
 
Answer
# 3
depending upon full load current of the load, the size of
cable is selected. Also calculate the % voltage drop and
see it is in permissible limit or not if is more select the
next highier size of cable.
 
Is This Answer Correct ?    33 Yes 9 No
Tauseef Tarique, Engineer(e)
 
Answer
# 4
FIRST FIND VOLTAGE DROP THEN FOR THE FORMULA


VD=MV*L*A/1000 WE GET VD
VD =VOLTAGE DROP
L=LENTH OF THE Cable
I =CURRENT IN AMP
 
Is This Answer Correct ?    21 Yes 4 No
Abdulsubur
 
Answer
# 5
A cable said to adequately sized when all the following
conditions aer satisfied:
1. Current carrying for steady state operation
2. Short circuit withstand capacity
3. Voltage Drop (steady state as well as during motor
starting)

As cable data provided by manufacturers/standards (ERA
report 69.30 etc) is for certain test conditions, which may
be very different from actual site conditions where the
cable is being installed.

Hence, to obtain the actual current carrying capacity of
the cable during steady state operation of the instalation
coditions of the cable shall be considered and suitable
derating factors (derating factor for group of cables,
Ambient temperature correction factor, derating factor for
thermal resistivity of soil, derating for depth of
installation) shall be multiplied to the manufacturer
supplied data. tehse values could be supplied by the
manufacturer or u can refer standards such as ERA 69.30 or
IEC.

The short circuit withstand level of the cable must be
greater than the energy let through value of the protective
device.
i.e. k2S2 >I2t where,
k = cable core insulation constant (143 for
XLPE)
S = Cable cross sectional area in mm2
I = Prospective fault current, rms in A
t = Disconnection time of protective device (in
seconds)

The voltage drop in A.C. cables shall not be more than 5%
based on the continuous maximum current loading and rated
voltage. During motor starting or re-acceleration the
transient voltage dip at the terminals of any motor will
not exceed 18-20% of the rated equipment voltage.

A cable of length L (km) having a resistance of RC (ohm per
km) and a reactance XC (ohm per km) operating in a three
phase ac system carrying a balanced current I (Amps) with a
power factor of Cos Φ will develop a voltage drop ΔV
(Volts):
1. For three phase ac systems
ΔV = √3 x I x L x (RC.Cos Φ + XC.Sin Φ)
2. During starting of 3 phase motors ( with a starting
current of IST at a power factor of Cos Φ) the voltage drop
will be:
ΔV = √3 x IST x L x (RC.Cos ΦST + XC.Sin
ΦST)

3. For single phase ac systems:
ΔV = 2 x I x L x (RC.Cos Φ + XC.Sin Φ)
4. For DC systems:
ΔV = 2 x I x L x RC
The percentage volt drop relative to the rated voltage is
given by:
Vd = (ΔV x VL) /100 %

Also, one may need to size the cable for earth loop
impedance considerations.
 
Is This Answer Correct ?    17 Yes 5 No
Dpl
 
Answer
# 6
Factors like the length of the cable, resistance, current
being carried by the cable , short circuit current, voltage
drop all come into play when selecting cable to be used.

First calculate the load current

I = P / x V x pf
pf =0,9 according to TCO Standard P-ST-2035, point 9.9

Then find apparent power

For three phase: S = x V x I
For single phase: S = V x I

Then I find the resistance by Ohm's law:

Z = V / I
V - is particular Load

Then find the short circuit current

I short circuit = S / Z

Then find cable size

S = I sh.circuit x / k k = 143, t = 1

And then select the cable according to the cable catalogs
 
Is This Answer Correct ?    3 Yes 0 No
Gulderaiym
 
Answer
# 7
verify motor capacity or kw 
Is This Answer Correct ?    7 Yes 5 No
Bala
 
Answer
# 8
Dear Friends,

cable types - XLPE/PVC /SWA

we have to choose the cable depend upon the applied
area/current rating

first step to find voltage drop for a required length as
per IEC regulation the VolDrop should not exceed 4% of
supply voltage it can be calculated

VD= mv/meter/amps this can be get it from cable chart -
supplier .if its ok then we can use

salah
 
Is This Answer Correct ?    7 Yes 7 No
Salah
 
Answer
# 9
Generally for copper cable sq.mm2 *2.5
for alluminum cable sq.mm2 *1.5
 
Is This Answer Correct ?    6 Yes 6 No
Muralidhara Kumar
 
Answer
# 10
wire size is depend upon the type of wire.
if we used the CU wire then the size of wire should be the 1/5 part of load current and AL wire wire will take around 1/4th of the load current
 
Is This Answer Correct ?    2 Yes 2 No
Rahul Singh
 

 
 
 
Other Electrical Engineering Interview Questions
 
  Question Asked @ Answers
 
a 25kvar capacitor bank connected to the secondary side of transformer.then why the capacitor draws more current then rated TATA 3
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.   3
what the different types of cables used for 11kv and 33kv over head work and what is the size of cable in sqmm.   2
hi... Can anybody give me description of type-2 coordination, IP protection, NEMA standards ? Thanks..   1
what do you mean by 1 ton in AC`s Bhel 36
Between AC generator(alternator) and DC generator which can be designed for high voltage and why?   1
what is the difference between cable routing and scheduling? Techno-Labs 4
what is the function of starter & choke in the tube light set & how choke give 1000 volts while switching on. IBM 11
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.   1
What are the various reasons for an inductin motor to get heated? Monnet 1
If two induction motors A and B are identical except that the air-gap motor 'A' is 50 % greater than that of motor 'B', then Lanco 2
how to calculate the ngr capacity(nutral grounding resistor) Divis-Laboratories 2
 
For more Electrical Engineering Interview Questions Click Here 
 
 
 
 
 


   
Copyright Policy  |  Terms of Service  |  Articles  |  Site Map  |  RSS Site Map  |  Contact Us
   
Copyright 2013  ALLInterview.com.  All Rights Reserved.

ALLInterview.com   ::  KalAajKal.com