the lowest value is not 0 to create a difference in between
broken ckt or any other error in ckt and actual min current
value.
b'coz for broken ckt or any other fault in ckt the current
o/p will be 0. means no current. but when it is 4 , then it
is the min o/p of the ckt and the ckt is running properly
both is confirmed.
the upper limit is a conventional one, no such reason behind
it. but it is a value practically can be achieved by the
designer easily.
4-20 ma could be taken it is followed by all manufacturers.
4 milliamp is used as span lower limit, because some
elements on the loop require power from the loop and
therefore a minimum level of power must be available
4-20mA :-
* Easy to find the open circuit(because this
signal level starts from 4mA, if the circuit in open the
output shows 0mA, so we can find easily the open circuit).
* Easy 0 to 100% segregation
4mA - 0%
8mA - 25% 12mA - 50%
16mA - 75% 20mA - 100%
* All manufacturer following the same standard.
0-20mA :-
* If it starts form 0mA, not able to find open
circuit easily.
3-15mA :-
* Less linearity, because 3mA is 0%, 15mA is 100%
so the deviation b/w 3-15mA is lesser than 4-20mA, So that
it reduces the accuracy of the measurement.
So that 4-20mA is preferred over 0-10v