ALLInterview.com :: Home Page KalAajKal.com
 Advertise your Business Here     
Browse  |   Placement Papers  |   Company  |   Code Snippets  |   Certifications  |   Visa Questions
Post Question  |   Post Answer  |   My Panel  |   Search  |   Articles  |   Topics  |   ERRORS new
   Refer this Site  Refer This Site to Your Friends  Site Map  Bookmark this Site  Set it as your HomePage  Contact Us     Login  |  Sign Up                      
Do you have a collection of Interview Questions and interested to share with us!!
Please send that collection to along with your userid / name. ThanQ
Google
 
Categories  >>  Engineering  >>  Electrical Engineering
 
 


 

 
 Civil Engineering interview questions  Civil Engineering Interview Questions
 Mechanical Engineering interview questions  Mechanical Engineering Interview Questions
 Electrical Engineering interview questions  Electrical Engineering Interview Questions
 Electronics Communications interview questions  Electronics Communications Interview Questions
 Chemical Engineering interview questions  Chemical Engineering Interview Questions
 Aeronautical Engineering interview questions  Aeronautical Engineering Interview Questions
 Bio Engineering interview questions  Bio Engineering Interview Questions
 Metallurgy interview questions  Metallurgy Interview Questions
 Industrial Engineering interview questions  Industrial Engineering Interview Questions
 Instrumentation interview questions  Instrumentation Interview Questions
 Automobile Engineering interview questions  Automobile Engineering Interview Questions
 Mechatronics Engineering interview questions  Mechatronics Engineering Interview Questions
 Engineering AllOther interview questions  Engineering AllOther Interview Questions
Question
Why Transformer in KVA?
 Question Submitted By :: Gaurav
I also faced this Question!!     Rank Answer Posted By  
 
  Re: Why Transformer in KVA?
Answer
# 1
actually rating of the machine (kva or kw) depends upon the 
power factor since the load power factor  to which 
transformer is supplying power is  not known , it may be 
capacitive ,inductive , or resistive that is why its rating 
is in kva and not in kw
 
Is This Answer Correct ?    63 Yes 12 No
Manoj Kumar
 
  Re: Why Transformer in KVA?
Answer
# 2
The unit of voltage in Volts
The unit of current in Amperes
When the energy transfer from primary ciruit to secondary 
circuit power is constant. there is no involvement of power 
factor. Due to this transformer rating in KVA not in KW
 
Is This Answer Correct ?    26 Yes 38 No
Naresh
 
 
 
  Re: Why Transformer in KVA?
Answer
# 3
As we know Cu loss depends on current & iron loss depends 
on voltage and not affected by power fector hence always 
transformer ratting defined in KVA not in Kw.
 
Is This Answer Correct ?    54 Yes 10 No
Nikunj
 
  Re: Why Transformer in KVA?
Answer
# 4
Since Transformer is a Static device and it is having two 
losses namely core loss and Cu loss. The core loss depends 
on the Voltage (V) only, where Cu loss depends on Current 
(I) only.So for this purpose the transformer always called 
its rating in apparent power only(VA).
 
Is This Answer Correct ?    39 Yes 7 No
Padmanaban
 
  Re: Why Transformer in KVA?
Answer
# 5
Because transformenr is used for converting voltage level 
only and nothing therefore its rating is in KVA i.e. KV x 
Amp It gives us rating/capacity of transformer how power it 
can handle.
The equipments not meant for consuming power are rated in 
KVA units & those consuming power are rated in KW.
 
Is This Answer Correct ?    7 Yes 28 No
Dileep
 
  Re: Why Transformer in KVA?
Answer
# 6
The instruments which converts energy from one form to 
another, rated in KW like motor etc which keeps same form 
of energy will be rated in KVA like Transformer,stabilizer 
etc
 
Is This Answer Correct ?    5 Yes 18 No
Amol
 
  Re: Why Transformer in KVA?
Answer
# 7
While designing the transformer manufacturer dosenot know 
the load power factor.
 
Is This Answer Correct ?    10 Yes 12 No
Sachin
 
  Re: Why Transformer in KVA?
Answer
# 8
The leading/lagging power factor has 
magnetizing/demagnetizing effect on armature reaction in a 
rotating electrical machine. Hence the losses depends on 
the load power factor. Unity PF has neither magnetizing nor 
de-magnetizing effect.

Whereas in a transformer, the power factor doesn't play any 
role in machine losses i.e. Cu & core losses are 
independent of power factor.

Hence the rating of transformer is always given in KVA and 
the rating of generators is given in kW at certain pf i.e. 
usually at 0.8 lag.
 
Is This Answer Correct ?    8 Yes 2 No
Pankaj Rajput
 
  Re: Why Transformer in KVA?
Answer
# 9
bcoz ..cu loss depends the current.iron loss depends the
voltage..so that total loss of transformer is depends
voltage,current...so the transformer ratings in KVA..
 
Is This Answer Correct ?    16 Yes 4 No
Saravana Babu
 
  Re: Why Transformer in KVA?
Answer
# 10
because its power factor depend on the other load.
 
Is This Answer Correct ?    6 Yes 3 No
Rakesh
 
  Re: Why Transformer in KVA?
Answer
# 11
Transformer is a static device having two type of losses 
such as ironlossed and cupper losess. since iron losses 
depends upon voltage(V) and cupper lossed depends upon on 
the curret(I) so rating of Transformer is in KVA
 
Is This Answer Correct ?    6 Yes 1 No
Niranjan
 
  Re: Why Transformer in KVA?
Answer
# 12
because trasformer is connected to supply resistive lode 
inductive lode &capaitive load .the power factor for those 
load is different (lag or leding )it worked apperent power.
the unit of apperent power is volt-aamper.that why 
transformer rated in kva.
(its my knowledge)
 
Is This Answer Correct ?    1 Yes 3 No
Nagaraj .n (bush King)
 
  Re: Why Transformer in KVA?
Answer
# 13
The X-mer o/p is limited by heating and hence by the losses 
in the X-mer. There are two kinds of losses in the X-mer: 
copper losses (ohmic losses) and iron losses. ohmic losses 
(I*I*R) depend upon current while core losses depend upon X-
mer voltage and are almost unaffected by X-mer P.F.. Hence 
the rated o/p is expressed in VA (V*I) or in KVA and not in 
KW.
 
Is This Answer Correct ?    2 Yes 0 No
Vidushi
 
  Re: Why Transformer in KVA?
Answer
# 14
The copper loss of a Transformer depends on current i.e. 
I^2 R and the iron loss depends on voltage. Hence the total 
losses depends on volt-ampere (VA) and not on phase angle 
between voltage & current.

Therefor the losses in a transformer are independent of 
power factor which is cosine of angle between voltage & 
current.

That's why the rating of transformers is in KVA and not in 
kW.

Now coming to Efficiency of a transformer: Yes it depends 
on power factor of load. Because the
Efficiency = Output/Input
           = (Input - Losses) / Input
           = 1 - (Losses / Input)
           = 1 - [Losses / (Vs * Is * Cos phi + Losses)]

Efficiency is inverted V curve (Y-scale) and the peak of 
curve appears between 50-60% load (X-scale)for various load 
power factors. Efficiency increases as the power factor 
increases.
 
Is This Answer Correct ?    7 Yes 1 No
Pankaj Rajput
 
  Re: Why Transformer in KVA?
Answer
# 15
kVA is the unit for apparent power. Apparent power consists 
of active and reactive power. Active power is the share of 
the apparent power which transmits energy from the source 
(generator) to the user. Reactive power is the share of the 
apparent power which represents a useless oscillation of 
energy from the source to the user and back again. It 
occurs when on account of some »inertia« in the system 
there is a phase shift between voltage and current. This 
means that the current does not change polarity synchronous 
with the voltage. But the heat generated in a winding as 
well as the eddy current losses generated in a transformer 
core depend on the current only, regardless of whether it 
aligns with the voltage or not. Therefore the heat is 
always proportional to the square of the current amplitude, 
irrespective of the phase angle (the shift between voltage 
and current). So a transformer has to be rated (and 
selected) by apparent power.
 
Is This Answer Correct ?    7 Yes 1 No
Krishnendran
 
  Re: Why Transformer in KVA?
Answer
# 16
because its load is variable. and motor load is 
continuously so we measure in KW. and Trans. measure in Kva.
 
Is This Answer Correct ?    0 Yes 0 No
Kishor A. Thakkar
 
  Re: Why Transformer in KVA?
Answer
# 17
we know
output=Input-Losess.   1

and the losess in transformer are two types ohmic, core 
losess and these are depends on the Voltage and secondary 
current , independent of P.F.

so the rating of losess is in VI not VICOSPIE.From equation 
1 losess in KVA so rating of T.F also in KVA.

Eg.if any machine connected at noload, the output put is 
zero, because of no current from below equation.
  VICOSPIE.

But in T.F there will be some power cosumption inform of 
loss.i.e. core loss.
 
Is This Answer Correct ?    1 Yes 1 No
Rajesh
 
  Re: Why Transformer in KVA?
Answer
# 18
because Transformer has Two winding.It becomes very hot 
while in running condition.So a considerable amount of heat 
loss occured.So the loss in Kw may vary.So Kw rating is 
avoided and Kva rating is given in Transformer nameplate.
 
Is This Answer Correct ?    1 Yes 1 No
Lalu Prasad Jadav
 
  Re: Why Transformer in KVA?
Answer
# 19
Rating of the equipment connected to T/F depends upon the 
power factor since the load power factor  to which 
T/F is supplying power is  not known , it may be any type 
of load (capacitive ,resistive , or inductive) that is why 
its rating is mentioned in KVA
 
Is This Answer Correct ?    1 Yes 0 No
R.emanuel James
 
  Re: Why Transformer in KVA?
Answer
# 20
transformer dosent consume power.it just step up/down the 
voltage.thats why transformer mentioned in kva
 
Is This Answer Correct ?    1 Yes 1 No
Rajesh
 
  Re: Why Transformer in KVA?
Answer
# 21
because transformer depends on voltage and current  v*i not
a depend of how much power is transfer so thats why its
rating in KVA.
 
Is This Answer Correct ?    0 Yes 1 No
Pritesh
 
  Re: Why Transformer in KVA?
Answer
# 22
kVA is the unit for apparent power. Apparent power consists 
of active and reactive power. Active power is the share of 
the apparent power which transmits energy from the source 
(generator) to the user. Reactive power is the share of the 
apparent power which represents a useless oscillation of 
energy from the source to the user and back again. It 
occurs when on account of some inertia in the system there 
is a phase shift between voltage and current. This means 
that the current does not change polarity synchronous with 
the voltage. But the heat generated in a winding as well as 
the eddy current losses generated in a transformer core 
depend on the current only regardless of whether it aligns 
with the voltage or not. Therefore the heat is always 
proportional to the square of the current amplitude 
irrespective of the phase angle (the shift between voltage 
and current). So a transformer has to be rated (and 
selected) by apparent power.
 
Is This Answer Correct ?    1 Yes 0 No
Omnarayan Tiwari
 
  Re: Why Transformer in KVA?
Answer
# 23
kVA is the unit for apparent power. Apparent power consists 
of active and reactive power. Active power is the share of 
the apparent power which transmits energy from the source 
(generator) to the user. Reactive power is the share of the 
apparent power which represents a useless oscillation of 
energy from the source to the user and back again. It 
occurs when on account of some »inertia« in the system 
there is a phase shift between voltage and current. This 
means that the current does not change polarity synchronous 
with the voltage. But the heat generated in a winding as 
well as the eddy current losses generated in a transformer 
core depend on the current only, regardless of whether it 
aligns with the voltage or not. Therefore the heat is 
always proportional to the square of the current amplitude, 
irrespective of the phase angle (the shift between voltage 
and current). So a transformer has to be rated (and 
selected) by apparent power.
 
Is This Answer Correct ?    0 Yes 0 No
Arvind Singh
 

 
 
 
Other Electrical Engineering Interview Questions
 
  Question Asked @ Answers
 
why do we need transformers?  5
pls tell about gas insulated substation?which gas is used for that substation?above which rating we are used this substation?how we take maintenance in that substation?it means substation fully shutdown or live condition?if live condition means how?pls clear this things Essar1
Why the generating station rating is in KW though the rating of generators in KVA? HAL5
what will happen if the secondary of current transformer kept open....  13
Wht is the meaning of floating neutral Cipla7
1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason  9
What is difference between 220v/50Hz & 120V/60Hz?  4
what is meant by leading or lagging power factor?like in capacitor power factor is leading and in inductor power factor is lagging  3
why are use star delta startor.  3
What is the meaning of ST and HT in electrical transmission and what are thier range.  3
1 tr is equal to how many Kw .is there any specific formula for this to get the result . NSN3
why we are maintain phase to phase clearence  3
What do you mean by S.F.U. unit? application of it.  9
HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM  7
about your self? Hyundai4
What is the maximum size(MVA)of power transformer available in the India/world? Adani7
WHY FLEXI LINKS ARE USED INBETWEEN GENERATOR TERMINAL OUTPUT & BUS DUCT CONDUCTOR.  3
what is RMU ?  7
every motors written in name plate IP 55 what is this?  2
What happen if we have run 415 V,50Hz designed motor at on 480V,60HZ  5
 
For more Electrical Engineering Interview Questions Click Here 
 
 
 
 
 
   