first u should know
1,The connected load of transformer or load factor
2,Highest connected load / motor in the transformer and its
starting type
3, diversity factor
because
KVA demand at 0.8 p.f =connected load x LF x DF
-------------
efficiency X p.f
starting current of highest KW load takes 6 times of full
load current. so we to check it whether the transformer has
the capability to feed the load or not during starting. its
the important thing while considering trafo selection..
first we calculate the industrial,ligthing & other load. on
that basis we can calculated the total load factor,on that
base we get a total kw ,and we get required total kva
Load Current,Load Voltage and Load Power factor(Secondary
Side). It may 3 Phase or 1Phase.
For 3phase Power in KVA = 1.732*V*I/0.8*1000
For 1 Phase in KVA = V*I/1000.
The rating of the transformer can be identified from the
above formula.