ALLInterview.com :: Home Page            
 Advertise your Business Here     
Browse  |   Placement Papers  |   Company  |   Code Snippets  |   Certifications  |   Visa Questions
Post Question  |   Post Answer  |   My Panel  |   Search  |   Articles  |   Topics  |   ERRORS new
   Refer this Site  Refer This Site to Your Friends  Site Map  Bookmark this Site  Set it as your HomePage  Contact Us     Login  |  Sign Up                      
Google
   
 
Categories >> Engineering >> Electrical Engineering
 
 


 

 
 Civil Engineering interview questions  Civil Engineering Interview Questions (3130)
 Mechanical Engineering interview questions  Mechanical Engineering Interview Questions (3300)
 Electrical Engineering interview questions  Electrical Engineering Interview Questions (13442)
 Electronics Communications interview questions  Electronics Communications Interview Questions (2385)
 Chemical Engineering interview questions  Chemical Engineering Interview Questions (420)
 Aeronautical Engineering interview questions  Aeronautical Engineering Interview Questions (77)
 Bio Engineering interview questions  Bio Engineering Interview Questions (17)
 Metallurgy interview questions  Metallurgy Interview Questions (80)
 Industrial Engineering interview questions  Industrial Engineering Interview Questions (165)
 Instrumentation interview questions  Instrumentation Interview Questions (2401)
 Automobile Engineering interview questions  Automobile Engineering Interview Questions (107)
 Mechatronics Engineering interview questions  Mechatronics Engineering Interview Questions (38)
 Marine Engineering interview questions  Marine Engineering Interview Questions (45)
 Power Plant Engineering interview questions  Power Plant Engineering Interview Questions (80)
 Engineering AllOther interview questions  Engineering AllOther Interview Questions (1204)
Question
why we generally use 3.5 core cable or in other word 1/2 
core for neutral and also confirm me that in balance 
conditiob(3 phase)current in neutral will zero
 Question Submitted By :: Electrical-Engineering
I also faced this Question!!     Answer Posted By  
 
Answer
# 1
In a three phase circuit theoritically there will be Zero
current in Neutral. But due to un-balancing of phases
practically phase voltage becomes unequal with the result
some current flows in neutral.That is why neutral is of
half rating only.
 
Is This Answer Correct ?    63 Yes 11 No
Dkmathur
 
Answer
# 2
Neutral conductor must be 1/2 the size of other
conductor.It is theoraticaly expalin that algebric sum of
all the phases when in balannce condition then neutral
current will be zero.
Now suppose one phase fail i.e total unbalace condition its
neutral conductor will provide a return path and its
current will be half the load on other phases.so by this
result on neutral conductor for every unbalance condition
its current will not exceed the rated than other phases.

Pardeep.kumar
Engineering Dept.
Panacea Biotec Ltd.
 
Is This Answer Correct ?    21 Yes 8 No
Pardeepkumar
 
 
 
Answer
# 3
Normally Neutral conductor is 1/2 the size of other
conductor.It is theoraticaly expalin that In a three phase
circuit ( Equal load in all three phasse) there will be
Zero current in Neutral, Ex. 3phase indusction load (Motor)
(NO NEUTRAL CONNECTED T OANY MOTORS AS THE RESISTANCE OF
THE THREE WINDINGS ARE EQAL).
But in a three phase to single phase distribution
(Resistive loads) it is not possible to maintain the equal
load in all three phases hence the unbalance current has to
be taken away from the circuit for the healthy opertion of
the equipmetns.
Thearitically and also practically it is prooved that the
flow of unbalance current in the 3 phase resistive load
distribution is always less than 1/2 of the phase current.
So 1/2 caore has been taken as a neutral
 
Is This Answer Correct ?    8 Yes 5 No
Raju Chetiar
 
Answer
# 4
The choice of whether to use a neutral of equal size to the
phase conductors depends on your design criteria and load
equipment. The difference of the load being delta, floating
star or star with a neutral point

A 3 phase circuit in balance will produce little or no
neutral current contribution.

However a 3 phase circuit imbalance will produce neutral
currents as per the following formula
A^2 + B^2 + C^2 - AB - AC - BC).

A three phase circuit wired in star with the neutral at the
star point will operate with null balance if the loads are
equal, it is possible (and I have seen this) for 2 phases
to fail and leave one phase connected to the load and
neutral. The neutral current becomes equal to the phase
current, the designer of the circuit failed to account for
this, the undersized 1/2 neutral overheated and caught fire
destroying the switchgear and damaging the furnace.

I would urge anybody to carfully consider all possible
outcomes when choosing neutral cable sizes as flames coming
out of a switchboard often alarms the unwary.
 
Is This Answer Correct ?    2 Yes 2 No
John Hancock
 
Answer
# 5
Generally it depend on load, If cable is used for inductive
load e.g.motor, if there is any fault then 1/2 core is
sufficient to carry fault current due to lagging power
factor. However, in resistive load we are using 4 core
cable since there is no power factor.
 
Is This Answer Correct ?    9 Yes 20 No
Sangekar Vaijnath
 
Answer
# 6
for using 3-phase supply in any instrument neutral is also
required since neutral capacity is just half to the phases.
we dont need to use 4 core thats cost matter..
 
Is This Answer Correct ?    0 Yes 23 No
Mritunjay Singh Yadav
 
Answer
# 7
Any switch mode power supply (computer, UPS, AC/DC
transformer) has some leakage current and imbalance. In
data centres they are starting to use full size neutral
cables to account for this. Basically only need 1/2 size in
motors, saves money on expensive copper
 
Is This Answer Correct ?    5 Yes 36 No
Blake Australia
 

 
 
 
Other Electrical Engineering Interview Questions
 
  Question Asked @ Answers
 
how we can find out the speed of fan without using any measuring instrument   2
what are adantages of OC and SC test over the load test?   5
advantage of using 110v than 230v NTPC 1
have u any web site who can give all electrical sum's to solve counting easy like how to convert 1kw=?Kva. Marriott 1
Find the octal equivalent for the binary number 101101110 Ecil 1
why distribution transformer are of DY11 type?   2
Name different types of fault and which instrument is used to measures earth,short,open cicuit fault? NTPC 6
Why should not we run the IM in low voltage, if runs means what will happen?(for example instead of 400V we give 250V supply)   2
why we changed the polarity of DC generator ? DMRC 1
WHAT IS MINIMUM AMOUNT OF CURRENT THE HUMAN BEING CANT RECOVER FROM THE SHOCK,WHAT IS THE RESISTANCE OF THE HUMAN BODY   3
why are we using resistor in NGR ?   1
what is ups Paralleling? how is load sharing at that time ? what are the things we have to note that time?   1
 
For more Electrical Engineering Interview Questions Click Here 
 
 
 
 
 


   
Copyright Policy  |  Terms of Service  |  Articles  |  Site Map  |  RSS Site Map  |  Contact Us
   
Copyright 2013  ALLInterview.com.  All Rights Reserved.

ALLInterview.com   ::  KalAajKal.com