For 415v,3phase,22kw rating of motor how to calculate MCCB rating
Answers were Sorted based on User's Feedback
Answer / ucmed_king
Refer Manufacturer coordination chart for required rating and model of MCCB.
There is a thumb-rule though. Convert KW to HP (KW/0.75), multiply it by 1.5 gives you the rated current. Multiply it by 1.5 for breaker value.
Here's the coordinartion chart:-
http://powertips-elec.blogspot.in/2010/11/selection-charts-for-dol-starters-l.html
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / akash
39Amp Per Phase is the actual load, but you can be on safer using side using 50/63Amp MCCB.
Is This Answer Correct ? | 6 Yes | 0 No |
Rated moter voltage and frequency is 380volt 60 hz but moter is running at 380votac 50hz is this harmful for moter winding
how to calculate the size of the HT cable
At what speed 1 HP motor can run an electric car of weighing 400 kg?
what is meant by IGBT how they differ from tyristor ?
WHAT HAPPEN IF LT SUPPLY 415 V FED TO THE HT 3.3KV MOTOR
What is instrumental error?
in case dc we mark as + ve & -ve..but in case a.c. we mark as ph&N...Y LIKE PLZ TELL ME
IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace.
How many turns are there in primary winding? (In Transformer)
difference between power surge and switching transient
what is the voltage between earth to neutral in lift.
What is turn ratio of a transformer?