if one potential missing in energy meter , how much % slow
the energy meter?
Answer / raul
If the potential coil is missing then the meter reading
will not advance i.e. the meter reading will stop
incrementing as the rotation of the energy meter disc is
dependent upon the interaction of fluxes created by the
shunt and series magnet with each other's induced current.
And when the flux created by the potential coil is absent
then the deflecting torque would be zero and hence the
rotating disc will not rotate.
Is This Answer Correct ? | 4 Yes | 4 No |
What happens if the series current double?
What is the difference between MCCB,ELCB,RCB & MCB
WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.
why the transformer ratings in kva or mva?
What is the use of Isolation Transformer, and Neutral is using for return path, finally this current is going.... but same time the voltage of the neutral should be below 1 V...
Define over current & earth fault ?how its functioning ?
which motor is used in electric train...???????
if the length, number of turns and area of coil are doubled then inductance of the coil becomes.?
At 765Kv, I have seen the use of PT at line side for metering and CVT for protection, although as far as my knowledge is concern, PT at this voltage level will have huge loss and more cost as compared to CVT as CVT can also perform same function of Protection and Metering? So my question is why use PT and not CVT for metering and protection in order to reduce the cost.
what do you mean by class PS CT and what are technical details needed for calculating it?
difference between diode and scr?
Hy the hydro power stations have high transmission and Distribution costs?