SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN
THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE
CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS
BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I
REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT
STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS
INITILAZIATION PLEASE HELP ME READRING THIS?
Answers were Sorted based on User's Feedback
Answer / warren emmett
Firstly, you should use a loop simulator and simulate the
Milliamp range to the dcs 0 to 20 or 4 to 20 do this in 25%
steps.If the dcs responds to the signal then the problem is
with the radar transmitter. If the problem persists when
simulating the the problem is on the Input card. Could be a
zero volt issue, a faulty input card or a wiring issue
could even be software related. To remedy the radar if that
is deemed faulty then consult the manual, you might need to
adjust parameters or do mapping of the vessel when it is
empty. Hope this helps
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / hirensinh
Set up the Parameter,Basically you know Tank is Empty or
Tank is Partially full.
Parameter set
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / prakash malviya
first u have 2 remove o/p wires of 4-20 ma then connect ma source with parellel this.then give 4& 20 ma...at 4 u see 0 %lvl & at 20 u find 100% lvl in dcs.if can't then u have 2 check from dcs side.in dcs check AI card particular channel for this.check wires grounding.
2nd condition if u find proper response in dcs with ma given to o/p wires..then go to the radar menu ..go to configuration..in that u find tank lvl...select full...then save it..
Is This Answer Correct ? | 0 Yes | 0 No |
Which products are available in the Mass Systemswitch and System Manager AC range?
if tx. dp increase or decrese what happend in the reading
WE Know that different supply voltage of solenoid valve like 24,110,220 etc..how we check the solenoid supply is 24v or 220 NOTE: No specification at device.
what is commisioning procedure,2)what is is the main work in commisioning in the field tx to dcs, plz send me detail
what is the relation between flow and pressure.for example relationship between level and pressure is p = phg like that i want ans for this question.and also how to calculate orifice sizing and flow transmitter. pls some one ans for this questions.
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
What is the formula To convert Degree centigrade to foranhight.
what is the output of conductivity sensor and PH sensor?
What is the PLC configuration in Cement industry?
why we are using drum level control valve air to close?
Hi, I'd like to know the purpose of MOS (maintenance override switch). At site, these switches are installed in a stanchion with the transmitter (connected to ESD). thank you.
3 Answers Adani, Adani Wilmar,
We are used ABB 800xa 5.1.please tell me how to instrall this.