what are the values to be accepted on 3 core 185sq mm for
11000volts on insulation resistance between conductors and
between conductors and earthed?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Normally we take 2M ohm /KV as sufficient IR
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / nikhil
1M ohms/kv + 1.
Eg: f0r 11 KV, 11+1= 12M ohms is ok.
Is This Answer Correct ? | 1 Yes | 0 No |
A.C. withstand voltage
Wet(ph/ground)
Time duration
KV
Mins
28 KV
1 Min.
Is This Answer Correct ? | 0 Yes | 1 No |
what is the Excaste meaning of CT Saturation?? 10 P 20, 15 VA, what is the meaning of 10, & 20. if the CT polarrity changed what will happened?? what is the differece between measuring CT & Protection CT?? what is the Saturation Point of measuring CT & Protection CT??
Why syn. Generators are used for the production of electricity?
Transformer Specification say 66/11KV, 23/27/35MVA OFDAN,what is OFDAN? we know ONAN,ONAF or OFAF
What are the advantages and disadvantes of delta and star connections in transformers and alternators?
Explain what is clipper and clamper circuits?
what is the difference between Resin Cast CT and Oil cooled CT?
what is the slip of synchronous motor
Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?
I have a generator of 300kw.400V,50hz . what is means can i assume the load Red Phase with Neutral 300kw.Yellow phase with neutral 300kw and Blue with neutral also 300Kw. or - red with neutral 100kw same as yelloe and blue phase also giving 100kw with neutral respectively
Why use in ht motore
How to do cable earhing? whether by grounding Armour to ground or by running extra G.I wire along with cable? which one is preferred mostly amoung them? If the second one is more preferable how many GI wires to be run along with cable (1 or 2)?
Why two nos. un-tensioned wires are placed inside the PSC poles used by powergrid in RGGVY works.