Dear sir,
we are getting voltage fluctuations suddenly for 2 or 3
minutes again it becomes normal. we checked each and every
connection some times we are getting 110 volts like that
from earth to neutral again it is reducing we are getting
supply from 45 kva DG set give earthing properly.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Unbalanced load can not be responsible for 110 V between
neutral and earth.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
Voltage between neutral and the earth indicates a loose
connection/joint in the neutral wire as neutral extends only
upto the point of loose connection.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / manoj dubey
generally voltage between neutral and earth occurs when
there is unbalance distribution of load in all three
phases. first check load balancing on phases. also check is
there any single phase heavy load is switched ON at the
time when voltage increases between neutral and earth.
Is This Answer Correct ? | 1 Yes | 1 No |
why m and c are shorted in wattmeter
what is specific gravity of a battery if specific gravity increase/decrease,what will happen to the voltage/current of the battery
what is the principle of synchronous motors?
What is the maximum load of 240mmsequre single core cable can carry?
PLC Training in chennai | PLC Training institute in chennai, PLC Training center in chennai | Best PLC Training in chennai | PLC Training course in chennai | SCADA Training in chennai | PLC Training in india
how do you select the ct/pt rating in substation
1 Answers Apollo, Shreem Electric Ltd, Tata Motors,
If one tertiary phase i.e. R,Y or B is earthed of a loaded type tertiary delta connected (Without load)of a power auto transformer, what is its advantage/disadvantage?
can we use HT cables for LT power supply ?
explain types of electric welding and its applications
Impedance relay is directional relay or non directional relay?
in conventional fan regulators how the current varies with speed?
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables