I am working in a process industry, in that there are
several sections devided in the SCADA screens and
individual sections may START independently. But sometimes
i am facing problem i.e, if section 2 Stopped by the
operator immediately Section 1 or Section 3 or Section 4 is
getting stopped can you expain the reason behind this?
Answers were Sorted based on User's Feedback
Answer / chandramauli sinha
There r various possibilities:
1. Its a common stop for all sections and are linked at
single command from SCADA screen.
2. Variable of section-1 is linked directly or indirectly
by process/ logic/ variable to other sections. On stopping
of Section-1, the process/logic of other section is
recognizing as fault and stops the respective sections.
please check that is there any link between these
sections...!
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / chandramauli sinha
There r various possibilities:
1. Its a common stop for all sections and are linked at
single command from SCADA screen.
2. Variable of section-1 is linked directly or indirectly
by process/ logic/ variable to other sections. On stopping
of Section-1, the process/logic of other section is
recognizing as fault and stops the respective sections.
please check that is there any link between these
sections...!
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jigs
It's possible if all sections are in operational interlock. If you stop one then other will be stopped.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jitendra chauhan
following problem may:
1. Is same interlock may used other sections?
2. have you checked stop command DO of all section, may that same DO?
3. may network getting stop, may PLC going to stop while given to stop command?
4. may that same stop command linked on SCADA?
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sks
this might be due to 2 reasons :
1)scan cycle of the processor has been increased anyhow as
the Dword value is updated after the signal is processed in
module. this extended scan cycle causes difference of
process values on HMI
2) check LAN ports of all stations and also the patch board,
if there is option for redundancy check the healthiness of
redundancy.
Is This Answer Correct ? | 0 Yes | 1 No |
I have 0.75mm sq multicore cable (IS type) , can use instead of same type but 1.5 sq mm cable ? Note : The distance is around about 150 meter.
what is the differnce betweeen hart and smart tx
Who to difference between analog in & analog out in dcs?
There is a problem with our HART475 it is not communicating with smart devices error becomes "NO DEVICE FOUND"we have insert 250ohm resistance as per requirement but invain plz tell me the solution?
How to work DCS? how to get the signal from Field Instruemtns to PIB to Console?
difference between repeatability and reproductability
how to calibrate the radar transmitter for measuring the exact tank level if tank is having agitator moving continiously because due to agitator tank surface level will vary every time.
how to turbine speed measurement?
0 Answers Jindal Steel and Power,
How to convert mmWc(mili meter water colam) to tph(ton per hour)?
who's take first position in process in the timing of new installation flow transmitter and control vavle. give the answer with logical trick.
what is orifice plate? Give me best answer?....plz
can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0 to 10 Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we will feed to the PLC.