what is dyn 11

Answers were Sorted based on User's Feedback



what is dyn 11..

Answer / dhiren

What do you mean by vector group of a transformer?
Ans:-
The vector group denotes the way in which the windings of a
transformer are connected and the phase position of their
respective voltage vectors.
The following examples are for two winding three phase
transformers:
So, what does Dd0, Dyn11, YNd5 etc. mean?
First symbol/symbols, capital letters: HV winding
connection.
Second symbol/symbols, small letters: LV winding
connection.
Third symbol, number: Phase displacement expressed as the
clock hour number.
The ANSI notations are not identical to the IEC marketplace
(See ANSI/IEEE Std C57.70). For the IEC marketplace the
winding connections are categorized as follows:
a) Delta (D,d)
b) Start (Y,y)
c) Interconnected Star (Z,z)
d) Open (III, iii)
Winding connection designations
High Voltage Always capital letters
Delta - D
Star - S
Interconnected star - Z
Neutral brought out - N
Low voltage Always small letters
Delta - d
Star - s
Interconnected star - z
Neutral brought out - n

Phase displacement
Phase rotation is always anti-clockwise. (international
adopted convention)
Use the hour indicator as the indicating phase displacement
angle. Because there are 12 hours on a clock, and a circle
consists out of 360°, each hour represents 30°.
Thus 1 = 30°, 2 = 60°, 3 = 90°, 6 = 180° and 12 = 0° or
360°.
The minute hand is set on 12 o'clock and replaces the line
to neutral voltage (sometimes imaginary) of the HV winding.
This position is always the reference point.
Because rotation is anti-clockwise, 1 = 30° lagging (LV
lags HV with 30°)and 11 = 330° lagging or 30° leading (LV
leads HV with 30°)
Dd0
Delta connected HV winding, delta connected LV winding, no
phase shift between HV and LV.
Dyn11
Delta connected HV winding, star connected LV winding with
neutral brought out, LV is leading HV with 30°
YNd5
Star connected HV winding with neutral brought out, delta
connected LV winding, LV lags HV with 150°
Some extra comments:
The phase-bushings on a three phase transformer are marked
either ABC, UVW or 123 (HV-side capital, LV-side small
letters)
Two winding, three phase transformers can be devided into
four main categories (Clock hour number and phase
displacement of those most frequently encountered in
practice in brackets)
Group I - (0 o'clock, 0°) - delta/delta, star/star
Group II - (6 o'clock, 180°) - delta/delta, star/star
Group III - (1 o'clock, -30°) - star/delta, delta/star
Group IV - (11 o'clock, +30°) - star/delta, delta/star
(Minus indicates LV lagging HV, plus indicates LV leading
HV)
Group I
Example: Dd0 (no phase displacement between HV and LV)
The conventional method is to connect the red phase on A/a,
Yellow phase on B/b, and the Blue phase on C/c. Other phase
displacements are possible with unconventional connections
(for instance red on b, yellow on c and blue on a) By doing
some unconventional connections externally on one side of
the trsf, an internal connected Dd0 transformer can be
changed either to a Dd4(-120°) or Dd8(+120°) connection.
The same is true for internal connected Dd4 or Dd8
transformers.
Group II
Example: Dd6 (180° displacement between HV and LV)
By doing some unconventional connections externally on one
side of the trsf, an internal connected Dd6 transformer can
be changed either to a Dd2(-60°) or Dd10(+60°) connection.
Group III
Example: Dyn1 (-30° displacement between HV and LV)
By doing some unconventional connections externally on one
side of the trsf, an internal connected Dyn1 transformer
can be changed either to a Dyn5(-150°) or Dyn9(+90°)
connection.
Group IV
Example: Dyn11 (+30° displacement between HV and LV)
By doing some unconventional connections externally on one
side of the trsf, an internal connected Dyn11 transformer
can be changed either to a Dyn7(+150°) or Dyn3(-90°)
connection.
Additional Note
By doing some unconventional connections externally on both
sides of the trsf, an internal connected groupIII or
groupIV transformer can be changed to any of these two
groups. Thus, an internal connected Dyn1 transformer can be
changed to either a: Dyn3, Dyn5, Dyn7, Dyn9 or Dyn11
transformer, by doing external changes on both sides of the
trsf. This is just true for star/delta or delta/star
connections.
Changes for delta/delta or star/star transformers between
groupI and groupII can just be done internally.

Is This Answer Correct ?    15 Yes 0 No

what is dyn 11..

Answer / bharatelectrical

dyn11 is vector group of transformer it it delta-star with
neutral with 30 degree phase shift it is used for
distribution transformer.

Is This Answer Correct ?    8 Yes 0 No

what is dyn 11..

Answer / kaustubh

dyn11 is vector group of transformer

Is This Answer Correct ?    3 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

How to work star delts method in the case of single phase motor?

4 Answers   Siemens,


need of capacitor used in plant

3 Answers  


What is line resistance of cable & how it can be measured ?

0 Answers  


why current flow to the opposite direction of flow of electrons???????????

0 Answers   Bhel,


How to size Air Circuit breaker (ACB)? What is the most important factors?

0 Answers   ABC,






I am getting diesel genset 62 kv for my house In addition there are 6 meters of 11kv for the house Lift also being installed for house plot sise 200sq yds total 4 + 2 foloors I want to know how much earthing required how deep it should be

2 Answers  


if we have 320KVA Genset kindly advice how much load we can put it.

0 Answers  


What is the difference between MCCB,ELCB,RCB & MCB

2 Answers   Bhel, HCL, HPL,


what types battery chargers are there?wanted with details.

3 Answers   SCS,


How to design constatnt power source with variable current and Voltage.

2 Answers  


Can I use measuring current transformers in protection purposes?

7 Answers  


In my power station 220 volts dc battery set. they coneected 84th cell taped

1 Answers   KPTCL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)