How to calculate & connection of 900KVA generator
2 sets & load(1500A)?
How to choose cable size and ACB size for this load &
generator?
please explain me detail.
Regards,
Mr.Han
Answers were Sorted based on User's Feedback
Answer / subra
ACB ------- 2500A
cable size = 630sqmm X two per phase one 630 sq mm for N total seven 630sqmm cable need
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / bala_vlsi
U Can select 1600 A breaker for incoming of D.G source
and u can refere cable calouge and select the suitable
cable for 1500A THAT TIME U SHOULD CONSIDER VOTAGE DROP
CALCULATION FOR THE SELECTED CABLE .
Is This Answer Correct ? | 5 Yes | 3 No |
wich type of cable is selected for wiring of 20hp motor?
block diagram of 2 ups system connected in parallel mode?
What is VVVF Drive ?
in cable joints procedure what electrical problems have been solved out ?
Why Two Transformers aside shoud be supperated by concreted wall?
HOW TO DO GRID EARTHING IN INDUSTRIES FOR A PRODUCTION BUILDING
30 kVA and voltage 380/220VAC how to find out kA?
The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is
Is it advisable to buy a plot for house construction near High Tension Power lines? If it so how much distance it should be away from power line? Iam residing at Chennai, Tamilnadu, India.
I want the details about BHEL company examination.Can anyone able to help me please.
How can we convert dc to equivalent ac??
What is the purpose of stand by earth fault protection for transformer ?