how to claculate earth strip size for 1500kVA transformer
for neutral and body
Answers were Sorted based on User's Feedback
Answer / chandan tripathy
As per IS 3043, Cross Section Area of Earthing Conductor
(A) =(If x√t) / K
Where:
t = Fault current Time (Second).
K = Material Constant.
Example: Calculate Cross Section Area of GI Earthing Conductor for System has 50KA Fault Current for 1 second. Corrosion will be 1.0 % Per Year and No of Year for Replacement is 20 Years.
Cross Section Area of Earthing Conductor (A) =(If x√t) / K
Here:
If = 50000 Amp
T = 1 Second
K = 80 (Material Constant, For GI=80, copper K=205, Aluminium K=126).
• Cross Section Area of Earthing Conductor (A) = (50000×1)/80
• Cross Section Area of GI Earthing Conductor (A) = 625 Sq.mm
• Allowance for Corrosion = 1.0 % Per Year & Number of Year before replacement say = 20 Years
• Total allowance = 20 x 1.0% = 20%
• Safety factor = 1.5
• Required Earthing Conductor size = Cross sectional area x Total allowance x Safety factor
• Required Earthing Conductor size = 1125 Sq.mm say 1200 Sq.mm
• Hence, Considered 1Nox12x100 mm GI Strip or 2Nox6 x 100 mm GI Strips
Is This Answer Correct ? | 25 Yes | 5 No |
you will follow as per State electricity board norms - 50
x 6 mm Cu for Nu and 50 x 6 mm GI FOR body 0r
you will calculate as per short circuit calculation
Formula 0.0054 x root t x I
Where
t =1 second
I = SHORT CIRCUIT CURRENT
example
Fault current- 33kA( assumed )
0.0054 x root 1 x 33000= 178.2 mm
so you will recommended 50 x 4 mm Cu
Is This Answer Correct ? | 14 Yes | 9 No |
Answer / k.prakashchandra
For above 750 KVA ,earth lead is determined as per I.S.1886
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / nitin
Mr. Bala,
what is 0.0054factor? Is it root3 divided by current rating
in A/sq.mm? Then for Cu it is 205 A/sq.mm and so root 3
divided by 205 comes to 0.0084. OK?
Is This Answer Correct ? | 0 Yes | 5 No |
What is MS-EXCELL?
Why reactors use before incoming of ac vvfd drive?
state the working of discharge lamp?
for testing busbar (33kv) hi-pot .whether we can apply DC r not.and what is the test volt for that .explain
Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?
why occ characteristics of generator is also called as magnatization characteristics ?
why T/F winding temp measurement cts are odd secondary current ie,109A/1.2A/1.4A?
0 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
How do we calculate the maximum amount of current in a 300 SQ.MM cable ?
If the Power Factor of generator is 0.85...What does this mean and Can the motors connected to this generator operate at PF more than 0.85 ?
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
in the directional overcurrent and earthfault protection,normally we are setting the angle 45 deg lead for phase fault overcurrent and -45 deg lead for earthfault fro forward direction.but both the fault are operating on the same angle region only.why?how the relay will response?
can we run a motor rated 50Hz,415vac,1440RPM At higher speed then rated on name plate with the help of VFD /drive on long term basis.wheater it will effect the motor life