ALLInterview.com :: Home Page            
 Advertise your Business Here     
Browse  |   Placement Papers  |   Company  |   Code Snippets  |   Certifications  |   Visa Questions
Post Question  |   Post Answer  |   My Panel  |   Search  |   Articles  |   Topics  |   ERRORS new
   Refer this Site  Refer This Site to Your Friends  Site Map  Bookmark this Site  Set it as your HomePage  Contact Us     Login  |  Sign Up                      
Google
   
 
Categories >> Engineering >> Electrical Engineering
 
 


 

 
 Civil Engineering interview questions  Civil Engineering Interview Questions (3157)
 Mechanical Engineering interview questions  Mechanical Engineering Interview Questions (3309)
 Electrical Engineering interview questions  Electrical Engineering Interview Questions (13489)
 Electronics Communications interview questions  Electronics Communications Interview Questions (2396)
 Chemical Engineering interview questions  Chemical Engineering Interview Questions (424)
 Aeronautical Engineering interview questions  Aeronautical Engineering Interview Questions (77)
 Bio Engineering interview questions  Bio Engineering Interview Questions (17)
 Metallurgy interview questions  Metallurgy Interview Questions (80)
 Industrial Engineering interview questions  Industrial Engineering Interview Questions (166)
 Instrumentation interview questions  Instrumentation Interview Questions (2409)
 Automobile Engineering interview questions  Automobile Engineering Interview Questions (109)
 Mechatronics Engineering interview questions  Mechatronics Engineering Interview Questions (38)
 Marine Engineering interview questions  Marine Engineering Interview Questions (45)
 Power Plant Engineering interview questions  Power Plant Engineering Interview Questions (82)
 Engineering AllOther interview questions  Engineering AllOther Interview Questions (1207)
Question
How can you calculate in detail the VA burden of current 
transformer used for Restricted earth fault protection? 
Please understand that the CT required here is Class PX or 
X. Also please show the calculations for knee point vtg, 
stabilizing resistor, magnetising current.
 Question Submitted By :: Electrical-Engineering
I also faced this Question!!     Answer Posted By  
 
Answer
# 1
Knee Point voltage is nothing but a point at which the CT
saturates. Thats why its always better to design the CTs
which can operate without saturation even at a voltage
appears in the CT during fault condition. Pls find below
the following formula for calculating the Knee point
voltage.

Vk=2If(Rct+2Rl).

where, If is the current refected to the CT secondary
during fault condition,

Rct is the resistance of the CT which can be adopted by
means of a thumb rule considering the CT ratio,

Rl is the lead resistance i.e. sum of the resistance of the
wire connected between the relay & CT and Impedance offered
by the internal circuitary of the relay

For PS class CT's designed considering the above,burden is
not applicable.
 
Is This Answer Correct ?    6 Yes 0 No
William Lobo
 
Answer
# 2
For PX class CTs , the burden is not normally mentioned .
There the CT is defiened based on the CT kneepoint
voltage , magnetising current etc . The burden is mentioned
in class P CTs

In PX class CTs the kneepoint voltage is normally based on
the max fault current and a diamensioning factor based on
system X/R ratio
 
Is This Answer Correct ?    3 Yes 2 No
William Lobo
 
 
 
Answer
# 3
Restricted earth fault protection is a differential scheme,
with CTs on the transformer neutral and phase leads. The
phase CTs are connected together in parallel & then
paralleled with the neutral CT. The resticted earth fault
(REF) relay is connected across the paralled CT circuits.

The relay is either a voltage operated device (eg Alstom
MFAC14)or a current relay with an external setting resistor
(eg Alstom MCAG14). In either case, the scheme is set at a
voltage based on the maximum voltage that is developed at
the relay for an external fault. A practical setting is
50% of the CT knee point voltage, if full info is not
available.
 
Is This Answer Correct ?    3 Yes 3 No
Williamlobo
 

 
 
 
Other Electrical Engineering Interview Questions
 
  Question Asked @ Answers
 
what are difference between indoor and out door substation   1
what is the formulae for selcting capacitor bank to increas pf   2
why we calculate only 11kv 33kv and 132kv ... why not 10kv 20kv 45kv? bhel 3
why motor run slow speed in star connection?explain how?   3
define reactive power? Alstom 2
what is power factor   3
megger how much voltage will produce ?   4
a bulb of 100W and anather bulb of 200W , rated supply voltage 230v.when supply voltage is reduced to 100v,which bulb will give more light? and why with calculation?   12
what is the difference between scaler and vector control in drive and where it is to be used ? Essar 1
what is different between relay and plc?   3
what is meant by slip & where its occur ? Lanco 5
how to select the rating of neutral ct with reference to transformer secondary current(in power transformer,stepdown tansformer,for example2000kva,11kv/415volt ASD-Lab 2
 