Answer / ashish tiwari
The HV cbale size shall be base on the fault level on HV
side. Like 18.4KA fault current for 11 KV supply & 21.34 KA
fault current for 33 KV supply. We can calculate the HV
cable
BY USING FORMULA ISH = K x A/( sq. root of T)
Where,
ISH :SHORT CIRCUIT CURRENT IN KA (r.m.s.)
T :DURATION OF SHORT CIRCUIT CURRENT IN SECONDS
A :AREA OF ALUMINIUM CONDUCTOR IN MM2
K :IS A CONSTANT = 0.094 for aluminium
ISH x Sq.rootT 18.4 x Sq. root 1
A = ------------ = ------------
K 0.094
= 195.7 sq.mm
HENCE 3 C x 240 SQ.MM XLPE (AL) CABLE IS REQUIRED FOR
INCOMING SIDE AS WELL AS OUTGOING SIDE OF 11 KV SUPPLY.
Is This Answer Correct ? | 32 Yes | 19 No |
Answer / ali
i want calcuiate the size of hv 6.6kv cable can trans 750 amper
with regard
Is This Answer Correct ? | 0 Yes | 0 No |
What are factors to be considered while we selecting the Core Balance Current Transformer for Earth fault protection
As load in a transformer increases, mutual flux linkage in core= A increases B decreases C not change D first increase then decrease
please explain working of revers power relay
Please tell me the formulaes while designing a substation for power Calculations in designing a 33 KV Substation?????
how many mega ohms insullation of the cable can't be use when testing with megger tester for Low voltage cable 240V use?
What is rotor angle stability?
how to select a capacitor, i mean we use 3.5 mico ferad cap for a celling fan,but how to select a cap for 1h.p motor,etc.........
Why does not AC excitation use in rotor of AC Generator instead of DC excitation?
As per which Indian Standard induction motors are manufactured?
what are the names of oil used in transformer and its chemical name?
What is purpose of APFC panel?
7 Answers Techno Electric and Engineering,
What is the basic rule for block diagram reduction technique?