How much KVAr bank reqired for 630 KVA transformer on full
load for maintain power factor upto.99
Answers were Sorted based on User's Feedback
Capacitor calculation is depends on load. if 630 KVA transformer is loaded fully with load p.f.=1 then no compansation is required but if the same is fully loaded with load p.f. = 0.8 then, kvar required is calculated as below:
KVAR = KW ( tanǾ1-tanǾ2); Ǿ1=old p.f.angle, Ǿ2=new pf angle
= 504 ( 0.75 - 0.14) [ here, KW=504 because, 630 X 0.8 = 504]
= 307.44 KVAR
say, 300 KVAR bank is required at load end for compansation
Is This Answer Correct ? | 15 Yes | 4 No |
Answer / engr junaid afrid
Simply says 630/2=315 kvar for your system.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mahendra singh
KVAR = KVA * sin@
KVAR = KVA * sqrt (1-cos@*cos@)
KVAR = 630* sqrt(1-.99*.99)
KVAR = 88.87
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / sanjay
generally kvar depends upon 33% of full load. please suggest if i m wrong.
Is This Answer Correct ? | 0 Yes | 2 No |
why universal motor work on ac & dc both?
What are the rating wise protections required for Generators from 600KVA to 2000KVA
how encoder works?
In India which type of PLCC IS used?
2 Answers Cipla, Ford, Jayashree,
in which direction real power and reactive power flow and why???????
Why the arms of delta in a delta-wye power transmission system are kept constant??
i need previous entrence exam papers of nhpc.
What is working Priniciple of TVSS ????
If ROC does not lies inside unit circle,then ? a) Fourier transform converges b) Z transform converges c) Hatly transform converges d) Colpit Transform converges.
What happens with squirrel induction machines if the ends of rotor conductors are kept open? Explain
what about the input current fan when regulator regulates to speed low?
Why DC excitation is used for alternators? Why cant it be AC?
35 Answers ABB, Ace Info, Alstom, Shalivahana Power,