How to protect the water pump by no load running.
Answers were Sorted based on User's Feedback
Answer / prakash
If your concerns with domestic water pump dry run control,
then you can use a floating switch at level point that can
be connected to series with DOL starter if already installed.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jimmy
Just put level switch NC contact in series with overload
contacts in the Starter Circuit.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kamal
By using under current relay , setting is no load current,
below this level it trip.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / parth belani
We can protect a pump from no load running by using a
minimum recirculation line. This line connects outlet with
the main tank or the inlet. so there will always be some
minimum flow through the pump.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sandip paithankar
put a moisture sensor in land which need to wet on starting and ending point of it.then give to transistor then micro controller do if else program and understand the condition of land it may wet or dry.then give command to relay to operate the water pump
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ks
by using the level transmitter and with out plc with some
no nc additional elements in the contactor it is possible
to control.
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / subrat.das1985
i think we can over come from this problem by using proximity sensor.or by using timer .
Is This Answer Correct ? | 0 Yes | 3 No |
why we are using in reverse power relay in generator singranizing
why bulbs when connected in series glow dim
what is a difference b/w earthing & neutral?
how we can improve power factor from 0.8 to 0.85 or 0.9 & how we identify its either lag or lead ? thank you
I need the recommended size for a 3 phase transformer at 13.8 KV Primary and connected loads of 3000 kVA at 4200 volts and 2375 kVA @ 480 volts AC.
How to synchronization will be done between two DGs ?
why it is so called as xlpe(cross linked poly ethyline) cable?
In Dyn11 power transformer if any one of the 3 phases connected to earth in star connected side then please explain effect of the current flow in delta connected side of transformer.(In this case if one phase is shorted to ground in star connected side then we observe the current flow in two phases only not three phases in delta connected primary side. Please explain why it is so?)
how to modify DOL control panel into Delta Y connection?
how ceiling fan worked?
sir i want previous entrance exam papers for written test
What core magnetic balance test of transformer? How to do this test in a three phase Star delta (star-LV, Delta-HV) transformer? How to measure and where to measure? thanks and regards Austin
22 Answers Neutech, Power Grid, TSSPDCL,