ALLInterview.com :: Home Page            
 Advertise your Business Here     
Browse  |   Placement Papers  |   Company  |   Code Snippets  |   Certifications  |   Visa Questions
Post Question  |   Post Answer  |   My Panel  |   Search  |   Articles  |   Topics  |   ERRORS new
   Refer this Site  Refer This Site to Your Friends  Site Map  Bookmark this Site  Set it as your HomePage  Contact Us     Login  |  Sign Up                      
Google
   
 
Categories >> Engineering >> Electrical Engineering
 
 


 

 
 Civil Engineering interview questions  Civil Engineering Interview Questions (3112)
 Mechanical Engineering interview questions  Mechanical Engineering Interview Questions (3298)
 Electrical Engineering interview questions  Electrical Engineering Interview Questions (13408)
 Electronics Communications interview questions  Electronics Communications Interview Questions (2381)
 Chemical Engineering interview questions  Chemical Engineering Interview Questions (421)
 Aeronautical Engineering interview questions  Aeronautical Engineering Interview Questions (77)
 Bio Engineering interview questions  Bio Engineering Interview Questions (17)
 Metallurgy interview questions  Metallurgy Interview Questions (80)
 Industrial Engineering interview questions  Industrial Engineering Interview Questions (165)
 Instrumentation interview questions  Instrumentation Interview Questions (2390)
 Automobile Engineering interview questions  Automobile Engineering Interview Questions (106)
 Mechatronics Engineering interview questions  Mechatronics Engineering Interview Questions (38)
 Marine Engineering interview questions  Marine Engineering Interview Questions (45)
 Power Plant Engineering interview questions  Power Plant Engineering Interview Questions (78)
 Engineering AllOther interview questions  Engineering AllOther Interview Questions (1201)
Question
Why restricted earth fault protection is needed? Why canít 
differential         
    Protection is sufficient?
 Question Submitted By :: Electrical-Engineering
I also faced this Question!!     Answer Posted By  
 
Answer
# 1
restricted earth fault protection is a protection scheme given in assistance to the differential protection.it is given to protect an earth fault which occurs very close to the neutral point in star connected windings of the transformer.this kind of fault a very low fault current only and this current may not be sufficient to activate the differential protection relays.
The sensitivity of the differential relays cannot be increased beyond a limit since this may lead to unnecessary tripping(the transformer may trip even for an earth fault occurring on the outgoing feeder Side)

Hence a special scheme of protection called REF(Restricted earth fault)is provided in order to protect a restricted area of the winding from internal earth fault.
 
Is This Answer Correct ?    22 Yes 0 No
Anaz.a
 
Answer
# 2
Due to the fact that current transformers always have a
certain error, the differential current always differs from
zero as soon as there is a load current flowing. Especially
during a through-fault condition with high short circuit
current , the differential current may be very high due to
the error of the current transformers. Depending on the
sensitivity of the setting value of the overcurrent
protection relay, when it is used as a simple differential
protection relay, unwanted tripping may occur.
For this reason, it is necessary to stabilize the
differential protection by means of a so called bias
current. For the restricted earth-fault protection using
the biased differential protection principle
 
Is This Answer Correct ?    0 Yes 4 No
Bandarawy
 
 
 

 
 
 
Other Electrical Engineering Interview Questions
 
  Question Asked @ Answers
 
what will happen if u run induction motor beyond its rated speed BARC 10
in power station power measuring unit is KW but in transformer is KVA why?   3
what is green house effect?   4
can induction motor becomes as a generator. if yes how it is possible. if there is a squirrel cage rotor.   6
sir please send me previous year questions of jspl through which i could prepare myself fpr the test. Jindal 64
why we are using DC violtage for testing of cables....which is used in HV AC applicatons...   1
WHAT IS THE COOLANTS IN TRANSFORMER? Bhel 7
Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of current?How can I calculate also when I have loads in KW? L&T 10
What is the function of restraining coil in differential relay? as well as restraining current? Siemens 4
draw a dol with the following rtds,stop/start,ct,vt and o/l supply is 6.6kv and the coil is 110v Anglo-Eastern 1
in power station what is the electrical circuit length of spacing between power transformer and lightning arrestors,for the voltage system of 230kv,110kv,33kv,22kv,11kv?   1
what is power and what is watts detailed description and formulas   2
 
For more Electrical Engineering Interview Questions Click Here 
 
 
 
 
 


   
Copyright Policy  |  Terms of Service  |  Articles  |  Site Map  |  RSS Site Map  |  Contact Us
   
Copyright © 2013  ALLInterview.com.  All Rights Reserved.

ALLInterview.com   ::  KalAajKal.com