findout of current?details 440v,3phase,085pf,hp-5
Answers were Sorted based on User's Feedback
Answer / sonali
7.5amps
GENERALLY WE TAKE 1.5 TIMES OF H.P
5*1.5=7.5A
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / naresh
rating =5*0.7457 =3.7285kw
vol =440v
3phase
current=(3.7285*1000)/(1.732*440*0.85) =5.755A
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / meraj
Given: v=440v, 3phase, pf=0.85, hp=5hp I=?
1hp=0.746kw
5hp= 5*0.746 kw = 3.73 kw
now P=3.73kw
for 3phase P=1.73*v*i*pf
I= P/(1.73*V*PF)
I = 3.73*1000/(1.73*440*0.85)
I = 5.76 amps
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / siva
power=1.732VIcos Pi
Hp to Kw
5x746=3730
I=3730/1.732*440*cos 0.85
I=4.89 A
Is This Answer Correct ? | 0 Yes | 8 No |
Answer / jim
p=vicos0
p=5*0.746
=3.73kw
i=3.73/(440*0.85)=9.973amps
Is This Answer Correct ? | 2 Yes | 11 No |
How to check 11000/1.732 to 110/1.732 Potentila transformer (PT)?
hi friends how 3 phase converter functioning ?what is working principle of rotory phase converter ?
What is accuracy of a measurement?
what is the value of current and voltage that our body can resist ?
if 1hp jet motar drop voltage when start from 220v to 120v give the reason and solution.
we all know that both the generator and motor are electromechanical conversion devices.....then why we rate motor in kw and generator in kva????
what is the different between rms and average value
is it possible to start a motor in felid connected to a remote mcc
What will happen to the protection and metering, if the polarity of a single or two PT/PTs in three phase system is reversed? Please provide reference if any.
If a motor of 8.5 KW with same load and using in both Star & Delta one by one,then which will take more current in star connected or in delta connected
difference between slippring induction motor and Generator?
how to select cable size according to ampere.