What is the purpose of taking Capacitance and Tan Delta
Test in Transformer bushing?
Answers were Sorted based on User's Feedback
tan delta (loss angle ) and cap is taken of the enquipment
such as CTs and TRF bushings wherein paper and other
material is utilised in its insulation.
tan delta and cap values indicates to you the condition of
the bushing insulation.
if a plot is plotted aginst the no of years of the bushing
in service and the value of tan delta taken every year, you
shall get the trend of insulation detoriation.
the higher side of tan delta value is 0.007.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / greg
tan delta gives the ratio of resistive current to capacitive
current.therefore it shows the amount of resistive current
flowing through the insulation,in other words it denoted the
dielectric strength of bushing.
Is This Answer Correct ? | 0 Yes | 0 No |
all the technical question with answers pleas send your email id ramar_eee@yahoo.com
draw tube light circuit
What happened if C.T mount at any cable or Bus bar in wrong direction . C.T going on proper work or not . C,T direction is essential thing to properly work.
why is corona loss greater in a stranded conductor as compared to a solid conductor ?
what is voltage ?
does the power factor of an induction motor improve upon used in parallel with a synchronous condenser , used commonly to provide a leading kva ?
how to select a breaker (MCB,MCCB,ELCB) for 18.5 kw, 3 ph. 480 v, 60 hz induction motor?
why fuse is not applicable for nutral and what will happen when it applied.
why induction generators are used in wind mills.why cant synchronous generators b used??
Conventionally, capacitors are considered to generate reactive power and inductors to consume it,how??????
why transmission lines traveled in high voltage?
for 1000kva transformer how kvar rating is need for this PFI plant. and how does it will calculate? and Apmpere rating of main cable connection?
6 Answers Engineers India, GCC, KP, QPSL, Siemens,